don_resqcapt19 said:I still fail to really understand why the possibilty of a path that is in parallel with the grounded conductor on the load side of the service disconnect is such a big problem, given that the code requires the creation of parallel grounded conductor paths on the line side of the service disconnect.
Don
The big problem with parallel paths is the imbalance of current. . If it's the earth itself or a steel conduit, the chances of having a problem are greatly reduced. . But if we're talking about conductors in parallel with each other, then we're talking 310.4
If the 250.32(B)(2) feeder neutral between buildings loses full contact on either end, not even a complete loss of contact but just a loose lug on one end, then the shield of the LV might pick up significant neutral/imbalanced current.
I've never heard of an inspector taking LV into consideration when considering 250.32(B)(2) and I'm not going to be the first one to do so. . I don't disagree with the concept of considering LV shields and would support it if asked, but I'm not going to jump out in front of the pack.