jasethomas
Member
What is the standard rule in assuming Grounding Conductor size in relation to the largest size current carrying conductor in a given assembly or piece of equipment?
For services see Table 250.66 & for others see Table 250.122. This may be what you're looking for. :smile:jasethomas said:What is the standard rule in assuming Grounding Conductor size in relation to the largest size current carrying conductor in a given assembly or piece of equipment?