Grrr!!!! Argh!!!!! Aaahhh!!!!

Status
Not open for further replies.

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Hospital Master Electrician
Try this one on for size. I'm going to keep this pretty mild, as I am mulling over inviting the inspector in question to this forum, as I believe some good would come of it.

I get a call to go to a house in a remote project this morning, which is already called for re-inspect and needs a correction. The info was vague. I get down there, and the card reads "Remove bare neutral from meter socket."

The service consists of a 200 amp 3R disconnect, connected to a lever-bypass meter socket via a 2" offset nipple.

I peer inside, and find a #6 bonding jumper running from an available terminal on the neutral/grounding bus, running through a bonding bushing on the offset nipple, and ending on the terminal on the meter enclosure. Nothing odd there. No bare neutral, all conductors insulated except for the grounds and bonding conductor.

Scratching my head, I get the inspector's # and tell him I see nothing wrong, please advise, I'm leaving in 15 minutes. He calls back and describes the bonding strap I didn't see on my first glance. It is connecting the load side neutral lug to the meter can, providing a parallel path for neutral, since a bonding jumper was also installed. Chastised, I remove the strap (which was tagged from the factory "Remove this strap if grounding is provided", duh) and get on my way.

After fixing it, I called him, left a message to the effect that I understand, good eye, good catch. I'll pass it on to my co-workers.

I found out this afternoon it failed again. Ticked and bewildered, I called him back.

"Did you reinspect the house?"
"Yes."
"I made the correction, why did it fail?"
"I wanted you to understand where I was coming from. I wanted you to remove the bare neutral from the meter socket."
"I removed the strap, breaking the parallel path to neutral. Why did it fail?"
"I'd prefer you to leave the strap, but remove the bare neutral, because that's the way everybody else in town does it."
"But the way it is now is code compliant. The strap was even labelled that it was to be removed in the event the can was grounded. So I removed the strap."
"I'll let it slide this time, but I'd prefer to see the strap used instead."
"I don't understand. It's code compliant, so why did it fail? My grounding is superior to the factory jumper, it wasn't even tight when I removed it!"

In the end, he agreed it was a compliant installation, but tried to imply he was doing me a favor by passing it. I have never been so profoundly irritated, at least not for a long time.

Interestingly, he asked me my name, and who I worked for again. I replied. I assumed it was a scare tactic, but didn't care. He then asked, "How long have you been in the trade?
"Two and a half years."

In surprise, he said, "You seem to have done your homework!"

I wish he would.

I'm so tempted to ask him here, because there have been a lot of non-code requirements from this man, and I don't believe he knows the code well enough as it is, to start "adding to it."

He said "I'm considering the lever-bypass meter as a disconnect." I felt compelled to inform him the function of that meter was to connect power independent of the meter, not to disconnect it. He repeatedly referred to the bonding jumper as a "bare neutral".

In the past, he has required (and we finally just gave in) that the receptacle under a jetted tub should not be supported per 314.23. He wanted them flopping under the tub, to aid in unplugging them. He has failed houses for not being able to find the temp GFI, there's no code requiring that, that I know of.

Enough already. Had to vent. Just surely glad I don't have to work in his jurisdiction again!!!

[ March 15, 2005, 11:07 PM: Message edited by: georgestolz ]
 
Re: Grrr!!!! Argh!!!!! Aaahhh!!!!

Ok, so I'm not done yet. :D

I wish I had thought of the range analogy when I was talking to him. Should I leave the jumper between ground and neutral on the range because the factory shipped it that way??? :D

He is very reasonable, and slow to anger, to his merit. But he will not bend, despite code references and argument, often times. I had to work in his jurisdiction last year for six months, and the lead guy on the job about went crazy with some of it.

(editted because I confused "hot" with "ground." :eek: )

[ March 16, 2005, 07:54 AM: Message edited by: georgestolz ]
 
Re: Grrr!!!! Argh!!!!! Aaahhh!!!!

I don't say stupid stuff like this often.

Your spector needs him a good ol' fashin reel style woopin out bak wer taint nobudy like is mommy to hep.

Ain't his job to stuff his ego by acting like the rear end of a horse.

If it weren't such a childish notion I'd say tell his boss on him. But I'll give you ten to one you wouldn't be the fisrt and it hasn't amounted to anything yet.
 
Re: Grrr!!!! Argh!!!!! Aaahhh!!!!

Originally posted by physis:
If it weren't such a childish notion I'd say tell his boss on him. But I'll give you ten to one you wouldn't be the fisrt and it hasn't amounted to anything yet.
It's been done. No effect.

Electrical inspectors should be required to spend 2 years in the field they are inspecting, IMO. That is lacking in this case. :(
 
Re: Grrr!!!! Argh!!!!! Aaahhh!!!!

No need. My job--that feels good--my job is thirty miles from his domain. I'm just thinking of those other poor sods out there. :D
 
Re: Grrr!!!! Argh!!!!! Aaahhh!!!!

Yeah, you only have to drive your happy butt out there to put up with his self importance hobby.
 
Re: Grrr!!!! Argh!!!!! Aaahhh!!!!

George sounds like he is a cousin of the little fat guy that I deal with.You know who I mean the one that as a kid had his lunch money taken every day and is now an inspector :D
One of our guys used to work with him and told me that when he was in the field as a service tech he was his helper and he has seen him cut the back of a cut in box off so the stud that the cultured marble top guys installed that was right there would clear ;)
 
Re: Grrr!!!! Argh!!!!! Aaahhh!!!!

Originally posted by allenwayne:
...But this guy has tagged receptacle spacing in hallways that he considered usable wall spacing 2 ft rule :D The funny part about that one is that the head honcho came out and said "Yeah, this is definutely a hallway." :D
 
Re: Grrr!!!! Argh!!!!! Aaahhh!!!!

You guys are lucky, at least your inspectors go out and inspect.
In one local town we work in we have to go to the inspectors place of business and bring him the building permit to get it signed.
Some real shoddy work goes on in that town without notice. Real scary.
 
Re: Grrr!!!! Argh!!!!! Aaahhh!!!!

Dang George, first you had issues with an inspector with no humor :D & now you have one with his own code agenda. Maybe there is something in the water. ;)
 
Re: Grrr!!!! Argh!!!!! Aaahhh!!!!

As an inspector, I can appreciate the frustation that contractors have when people try to enforce more than the code allows. I have made the same mistake on a few occasions and have been politely corrected by the electrical installer. More often than not, the work exceeds the code provisions and when I point out certain issues, the installer tells me they won't do it to code, they will do it better than code. I have always appreciated the conversation and additional knowledge that I receive in the field. I worked with the electrical trade for 8 years prior to taking this position in 1989. Mostly residential and light commercial. I still strugle with some industrial applications. Inspector are human, even thouugh some seem less human than others.
 
Re: Grrr!!!! Argh!!!!! Aaahhh!!!!

Originally posted by georgestolz:I'm going to keep this pretty mild, as I am mulling over inviting the inspector in question to this forum, as I believe some good would come of it.
Quit mulling, and do it. I am sure it would serve the interests of the industry, even if he declines the invitation.
 
Re: Grrr!!!! Argh!!!!! Aaahhh!!!!

Inspector 102,

Most inspectors I deal with have the same temprement as you do. Occationally they'll call me on something they think is wrong (of course it never is :D ) and we actually rather enjoy going over the codes together.

And when they know you're gonna get the code book you can do just about anything you want. What that? I'll go get the code book "no that's alright, I'll take your word for it" but it's just ou.... "that's ok I'll just sign this" here, I'll get it "too late, already signed". :D
 
Re: Grrr!!!! Argh!!!!! Aaahhh!!!!

I am asuming that the inspector in question is a state inspector just like the one i deal with every week, They seem to take J.H.A to the Nth degree.
 
Re: Grrr!!!! Argh!!!!! Aaahhh!!!!

How's this: (Hope it's okay, I sent it. :D )
(His name), (p.s., this ain't a sales pitch, it's free)

I am writing to invite you to join the Mike Holt Code Forum, where we discuss the NEC in all it's power and wisdom. It's a forum exclusively for electricians, contractors, inspectors and engineers to discuss code issues.

When we spoke a few days ago, you said that "I'd been doing my homework." Well, that's where I study. There are some very intelligent people on that site, and I have learned volumes in the short time I have been there.

I have a hidden agenda for asking you to join. I no longer work in (your town), I was just catching the corrections on (that house). But I have worked there in the past, and I recall our electricians going head to head with you on certain issues. Holt's site is a good place to either gain supporting information on why you are right, or correction when perhaps you are wrong.

In our normal surroundings, you are an inspector and I am an electrician, leaving us on uneven footing. Electricians will tell you anything to not have to come back and make corrections. There is no agenda like that on a neutral and informed site like Holt's.

Please see what I mean at http://www.mikeholt.com/codeforum/ultimatebb.php

I mean no disprect in writing this. I enjoy code, and I imagine you do too.
George Stolz, RW
 
Re: Grrr!!!! Argh!!!!! Aaahhh!!!!

Hey George, I checked out that link you posted and all I found was a bunch of self absorbed wind bags. One guy called Phyllip or something was especially insufferable. :D

Well, I hope he accepts your invitation. We could always use more inspectors. I like to get their perspective and there aren't that many here, at least that post.
 