H.P to Volt amps
nizak
what would the equivalent volt amperes be for the following motors
1/4 hp
1/3 hp
1/2 hp
Using 746 watts/1hp does not seem to yield the proper answer.
These three values were listed on a worksheet that my nephew has from an electrical class he's taking at the local skill center.
There was no other info offered other than these are 120V motors.
1/4 hp
1/3 hp
1/2 hp
What you are missing for finding actual input power is efficiency and power factor.
per NEC however you use tables at end of art 430 for standardized motors listed there - they go by worst case efficiency/power factor motors you are likely to find for determining minimum conductor ampacity.