Handhole Cover Bonding

Status
Not open for further replies.

camaelec

Member
2007 NEC Article 314.30, paragraph (D) requires metal handhole cover to be bonded in accordance with 250.96(A). 250.96 (A) states that metal raceways, cable trays....and other non-current-carrying parts "that are to serve as grounding conductors" shall be bonded. Is a metal handhole cover considered a non-current-carrying part intended to serve as a grounding conductor?????
 
Handhole Cover Bonding

Correction.....2005 NEC. We only work with schools in California and the code used is the CEC, 2007. Sorry.
 
Is a metal handhole cover considered a non-current-carrying part intended to serve as a grounding conductor?????

I would say yes, in the sense that if the cover were to be inadvertently energized it should be connected to, and be part of the, equipment grounding conductor fault path.

There have been numerous accounts of people being electrocuted due to metal handhole covers not being properly bonded.

Chris
 
Yes. The 08 NEC changes this to connected to an equipment grounding conductor. The intent is the same.
I will tell you that there are thousands and thousands of metal handhole lids and frames that are not bonded. Many are energized and just waiting for some one to get shocked.
 