- Massachusetts
Don't forget that a two pole breaker without a handle tie can also have only a single handle. Common in fact in larger sizes
True, and very common with Square D breakers in the small sizes.
If you ask me, the bar connecting the two poles of most two-pole breakers is a handle tie. It's kind of ridiculous to suggest otherwise.
We are mixing things up. The OP wanted to know if a two pole breaker is allowed on a MWBC. It is, without a doubt.
You and I and Bob are arguing about using switches.
Thanks Dave. I see that but reading item 1 which references multi wire branch circuits, it doesn't say a 2 pole can be utilized in a multi wire branch circuit. I'm going to speak with our AHJ. If the book doesn't specifically state it, he doesn't allow it.
Sent from my SM-N920V using Tapatalk
Well you and Bob are crazy so I just skipped over your comments. Actually in the handbook it does say that you may use a 2-pole switch. The code language on the other hand does not mention it.Yes because Bob brought that up and I thought there was something I was missing in the NEC. I was asking how he came to that interpretation. I don't see it
I see using a switch as a practical solution to meet code on old fuse panels.I would certainly think that a dp switch would be okay I just don't see the wording. That is why I was asking if there was an exception somewhere. Oh well.
I don't disagree with you and again, the handbook is not the code. Just telling you what it says.I would certainly think that a dp switch would be okay I just don't see the wording. That is why I was asking if there was an exception somewhere. Oh well.
It simply says a means to disconnect all ungrounded conductors at the source.
And Dennis' point is that a switch is not disconnecting the circuit at the source, it is disconnecting it near the source.
A subtle difference, but it is there.
I could not disagree more.
The source is at the OCPD locating a switch beside the panel is at the source
If they meant specifically the OCPD had to open all poles that is what it would say as it does in say aticle 240.
This whole idea that it must be a breaker really blows my mind. Never have I heard anyone express that opinion before this thread.
I cannot wrap my head around it in the least.
I think they needed to leave an option for MWBCs that are supplied from old fuse panels.
Your words back in 2008:
Yes, my words in 2008 saying the same thing I am saying now.
There is nothing in the wording preventing up the use of a switch.
We will have to disagree. The source isn't the switch no matter how you look at it. The source of the circuit is at the overcurrent protective device.
2-32 Log #598 NEC-P02 Final Action: Reject
(210.4(B))
Submitter: Herbert S. Pharo, Cape May, NJ
Recommendation: Revise text as follows:
Each multiwire branch circuit shall be provided with a means that will
simultaneously disconnect all ungrounded conductors nearest At the point
where the branch circuit originates.
Substantiation: The problem is that the point where the branch circuit originates is at the overcurrent protective device. Nearest as used in 230.70(A) (1).
The new word will make it clear that the disconnect need not be overcurrent protective device.
Panel Meeting Action: Reject
Panel Statement: The term “nearest” is vague and unenforceable. The present language is clear and enforceable by the authority having jurisdiction.
Number Eligible to Vote: 12
Ballot Results: Affirmative: 12
In your scenario I can have a switch 100 feet from the panel and it would be compliant since no distance is given.
Using Charlie's Rule I honestly cannot see it any other way -- obviously you do so we will have to agree to disagree.
Appreciate all the professional opinions. The AHJ allowed the use of a DP breaker. To comment on the statement if the NEC doesn't say you can't then you can didn't work here in NC.