Using SJO, cord-plug, str relief conn or an appliance cord is not a violation of 110.3(B).
All the componants used to make or use a cord set for an appliance are UL listed for the purpose and are not violations of the NEC. If this was the case, we would not be able connect any of these types of appliances. Ranges, Dryers, Disposals, Cooktops, etc. all fall into the same installation type.
I have never had an inspector question using a cord set to connect an appliance to serve rule in Art. 422.16(B)(2)., if the unit does not comply with Art. 422.34. In my opinion, I don't see how you can hard-wire a dishwasher in the first place and be legal, possibly using ENT if the raceway is less than 3'.
Now installing so-called floating switches, using NM as an alternative to a cord, are violations of Art. 314, 334, etc.
Art. 334.30 Securing and Supporting states in part "shall be supported and secured by staples, cableties, straps, hangers or similar fittings within 12 in. of boxes"
How are you going to comply with this using NM to hardwire a dishwasher???
Come on guy's were supposed to be licensed professionals and we should be using some common sense as well as neat and workman-like installations.
Mark DuVerger
Mark's Electrical Service