Can you quote the section that would allow that? The way I read it, 50A is the largest receptacle allowed.
So 625.44(A)(3)
"grounding-type receptacle outlet rated at"
"250 volts, single phase, 30 or 50 amperes" or
"125/250 volts single-phase 30, 50 or 60 amperes"
..
Do I now read that correctly that 3-wire is OK for 50A but 4-wire is required for 60A? What use is the neutral at that point?