Hi all
in a health care facility (surgical center)
we used hospital grade BX (2 grounding paths)
and we terminated the green wire of the bx to the 1900 metal box
and we used hospital grade self grounding outlets within ¼" of the face of the box
the inspector is telling us that we have to connect the green wire to the outlet and not to the box no matter if we're using self grounding outlets
however i don't think that he is right since the outlet is self grounding what difference does it make if it is connected to the outlet or to the box?
this is not a mulberry cover
it is a regular installed dressed box with a self grounding outlet and face plate
Let me know your thoughts
Thanks all