I am bidding a job to install 5 geothermal (pool) heatpumps
RLA 23.2, Max OCD 40, Min circuit 29.3
Voltage is 120/208 3-phase.
Question is finding the subpanel that needs to be installed.
430.24 states 125% FLA plus other FLA
so total load is 23.2 x125% +23.2+23.2+23.2+23.2=121.8A conductors
breaker for subpanel is
430.62 125% Max OCD plus other FLA
so breaker is 40 x 125% +23.2+23.2+23.2+23.2=142.8A so 150A breaker
Would a 150A panel be sufficent with 150 amp main with #1 copper conductors, or do I add an addtional 125% on each item due to 215.3,etc states that you must size equipment/conductors 125% of continous load (80% of equipment capacity)? This would then make this a 200A breaker/Panel with 2/0 copper conductors.
Any input is greatly appreciated. Thank you
RLA 23.2, Max OCD 40, Min circuit 29.3
Voltage is 120/208 3-phase.
Question is finding the subpanel that needs to be installed.
430.24 states 125% FLA plus other FLA
so total load is 23.2 x125% +23.2+23.2+23.2+23.2=121.8A conductors
breaker for subpanel is
430.62 125% Max OCD plus other FLA
so breaker is 40 x 125% +23.2+23.2+23.2+23.2=142.8A so 150A breaker
Would a 150A panel be sufficent with 150 amp main with #1 copper conductors, or do I add an addtional 125% on each item due to 215.3,etc states that you must size equipment/conductors 125% of continous load (80% of equipment capacity)? This would then make this a 200A breaker/Panel with 2/0 copper conductors.