Most of the stuff here has been asked before in some form so ask away.![]()
Well, I read most of the 72 pages.
I guess my thinking, however incorrect it might be, is that if the maximum fuse amps or maximum circuit breaker as stated on a refrigeration unit is used, then the wiring ampacity to the disconnect and the breaker at the main panel would need to be based on that maximum. So, if MOCPD is listed as 30 amp's, then the the circuit breaker should be 30 amp, and the wiring should be sized for 30 amps..
If the minimum circuit amp's. as listed on the name plate is used (call it 18.7 amps), then the branch wiring to the disco and the breaker in the main panel for the circuit could be based on that minimum circuit ampacity (18.7 amps).
I have no problem understanding having a 30 amp. breaker in the main panel with wiring sized for 30 amps going to a fused disconnect with 20 amp fuses in this case.
What I don't understand is the concept of running wiring for the circuit that meets the minimum circuit amps (18.7 amps), but protecting it with a breaker sized on the maximum circuit breaker (30 amps.). From reading the comments in the 72 page thread, the argument for using wiring for 20 amps., with a 30 breaker could be done because the unit should not have an actual run load of more than 20 amps.. Although that might be true, I can't see where the NEC allows for this, nor do I understand the desire to use a 30 amp breaker instead of a 20 amp breaker. The so called nuisance trips are usually an indication of a system problem that otherwise hasn't been identified.