Greetings Tommy,Where is that code Art.
I think what they are trying to say is Type MC Cable is acceptable as long as it meets the requirements found in Section 330.10(A)(11).
330.10(A)(11) In wet locations where a corrosion-resistant jacket is provided over the metallic covering and any of the following conditions are met:
a. The metallic covering is impervious to moisture.
b. A jacket resistant to moisture is provided under the
metal covering.
c. The insulated conductors under the metallic covering
are listed for use in wet locations.