As a space saver, and cost saver, I do not believe he needs to tap/parallel 250's, he could use considerably smaller conductors.
If you were paralleling for a 400A overcurrent device, what size conductors would you install?
No.
Order the correct lugs for the breaker.
What code would you use to back up this statement?
You kidding or serious?
110.3(B)
Technical reason: since all stranded conductors have an odd number of strands, there's no way to make an exact 50-50 split.I'm not try to be argumentative but I personally have been in this situation before where one of my techs split an 8AWG to two terminals of a terminal strip. It's up to me to PROVE it violates the installation listing.
Technical reason: since all stranded conductors have an odd number of strands, there's no way to make an exact 50-50 split.
To support Bob's "where's the rule it has to be a 50-50 split", as long as all strands are terminated, you have not reduced the cmil size of the conductor. Amperage should divide among the strands by the ratio of strands landed per terminal to all strands.Technical reason: since all stranded conductors have an odd number of strands, there's no way to make an exact 50-50 split.
To be honest it's one of things that seems obvious and I wouldn't consider doing it. However to use 110.3(B) wouldn't the manufacutre have to specifically say 100% of the conductor connected to the terminal must be used... or something along those lines.
I'm not try to be argumentative but I personally have been in this situation before where one of my techs split an 8AWG to two terminals of a terminal strip. It's up to me to PROVE it violates the installation listing.
Alright let's say there is a weird situation where someone brings a stranded wire into a receptacle outlet box and splits the conductor to to two receptacles. How do you prove the installation isn't "installed and used in accordance with any instructions included in the listing or labeling." for the receptacle?
It may seem common sense but proof is required.
I didn't say it was a good reason.OK, where is the rule that requires a 50-50 split.![]()
What you posted is the UL 486a-486b scope for Wiring Connectors.How about this....UL 486 is what the manufacturers of terminal lugs meet.
...
UL Standard for Safety for Equipment Wiring Terminals for Use with Aluminum and/or Copper Conductors,
UL 486E
Scope
These requirements apply to pressure type equipment wiring terminals intended for use with appliances or equipment with either copper, aluminum, or copper-clad aluminum wire in accordance with the National Electrical Code, NFPA 70. The terminals may be constructed so that they are also acceptable for use with any wire.
These requirements apply to field wired equipment wiring terminals which are an integral part of the equipment, or are intended for use in specific equipment.
These requirements cover ampere-rated equipment wiring terminals, horsepower rated terminals and wire range rated terminals, intended for use in appliances and equipment and that comply with the requirements for such appliances and equipment.
These requirements cover terminal-type wire connectors intended for use with No. 12 AWG (3.3 mm2) or larger aluminum or copper-clad aluminum wire, and for No. 30 AWG (0.05 mm2) or larger copper wire. Current ratings are based on the ampacity of insulated conductors rated 75?C or 90?C in accordance with the connector rating and not exceeding the maximum current rating - if provided - of the wiring terminal. For equipment wiring terminals intended for use with stranded conductors, the following conductor strand configurations are intended:
Aluminum - Class B concentric, compressed, and unidirectional lay compact.
Copper - Class B concentric and compressed, Class C concentric.
Copper-Clad Aluminum - Class B concentric.
Other class and strand configurations may also be covered as indicated by marking.
These requirements also cover connectors additionally rated for No. 2 AWG (33.6 mm2) and larger compact-stranded copper conductors. These connectors are identified in accordance with . See also and the Exception to (b)(3).
These requirements also cover connectors of the types specified in intended for use with metric conductors that have cross sectional area within the range of the rated AWG/kcmil conductors. For example, a connector rated for 6 AWG - 250 kcmil may additionally be rated for 16 - 120 mm2. See , , , and .
These requirements do not cover insulated connectors, binding-screw terminals, built-in terminal connectors on devices rated under 30 amperes and intended for outlet-box mounting or having provision for strain relief, or built-in terminal connectors on devices having integral cable clamps.
A product that contains features, characteristics, components, materials, or systems new or different from those covered by the requirements in this standard, and that involves a risk of fire or of electric shock or injury to persons shall be evaluated using appropriate additional component and end-product requirements to maintain the level of safety as originally anticipated by the intent of this standard. A product whose features, characteristics, components, materials, or systems conflict with specific requirements or provisions of this standard does not comply with this standard. Revision of requirements shall be proposed and adopted in conformance with the methods employed for development, revision, and implementation of this standard.
UL 486E does not reference any other UL Standards.
Tap 2-250 with one of these>>>>>>>>>>>http://www.polarisconnectors.com/37022_POLSAL_EXTRA_IPL1.pdf
I wonder if the original post got the electricity turned on.
Since the code does not specifically say, a stranded single conductor cannot be unraveled and split into to two conductors and landed into 2 lugs....and UL says there is a way UL list conductors terminating into lugs, but other ways may be ok....
Then whether this is acceptable or not is up to the AHJ, and their interpretations as defined in NEC 80.13.
I wonder if the original post got the electricity turned on.
Since the code does not specifically say, a stranded single conductor cannot be unraveled and split into to two conductors and landed into 2 lugs...
and UL says there is a way UL list conductors terminating into lugs, but other ways may be ok....
Then whether this is acceptable or not is up to the AHJ, and their interpretations as defined in NEC 80.13.
My guess is yes, but what he had to do to get it turned on is what I think everyone, including myself, is interested inI wonder if the original post got the electricity turned on.