help!! old lv lighting
electricmanscott
Boston, MA
Massachusetts Master Electrician, one man show.
Trouble shooting old lighting system. Push button controls relay at fixture. Any tips?? All lights are not working.
I have not seen a system like that in a long time. There was a central transformer that runs the system. Did you check it out? On one site I could not find out why the system had completely dropped out until I discovered that they installed a new sliding door and cut all the low voltage cables.
If nothing is working I would also make sure the trany has power and check the output on the secondary side. It is very unlikely all the relays and switches don't work so I agree the trany seems to be the problem.
24v tranny puts out 27v without load connected. With load connected it drops to 11v and gets burning hot. Time to go hunting
I actually kind of liked these systems and wish they weren't considered old news. Maybe because they were sort of unique.
Happy hunting.
Five hours, gallons of sweat, lots of fibreglass ingested, problem solved. Found the short. The last fixture in the loop. :roll:
I always start in the middle. :)
Yes logical, I suppose. If there were say 32 fixtures, you could locate the faulty unit by eliminating all others in 5 steps instead of up to 31.
But then there are the practicalities. In the absence of any better clues, most of us would check what's quickest and easiest first.
Ever stop to wonder how many times the problem is in the last item in the circuit?
I've observed that Murphy's Law rules.
I've observed that it doesn't matter. . . [irony] with the middle as the first, there is still a "last". [/irony]
Murphy's Extended Law: If a series of events can go wrong, they will do so in the worst possible sequence.
I'm impressed. It's been 105? here and I have to work at least 10 hours to sweat 2 gallons.:grin:
Troubleshooting school says 2 independent faults are a rare occurrence. I've seen the opposite many times. Instead of the middle of the string, I would have started at the lum with the burned out lamp!:roll: