Re: HELP !!!! outlet placement?
Re: HELP !!!! outlet placement?
As I said earlier, that is only true for the "kitchen, family room, dining room, living room, parlor, library, den, sunroom, bedroom, recreation room, or similar room or area." It is not true for hallways. 210.52(H).
Re: HELP !!!! outlet placement?
No.Originally posted by electricmanscott:Yes.Originally posted by LMaloney: In a single family dwelling, is an outlet required by the NEC within 6 feet of any doorway.
As I said earlier, that is only true for the "kitchen, family room, dining room, living room, parlor, library, den, sunroom, bedroom, recreation room, or similar room or area." It is not true for hallways. 210.52(H).