Keep in mind the temperature when you install it. If it's hot, it'll be mostly shorter; if it's cold, it'll be mostly longer.
kwired
Electron manager
NE Nebraska
Had to read that twice. ;) I think you meant if its hot on the install then it will get shorter when cold.
If you read instructions for the expansion fitting they usually mention this, you need to set the thing at installation according to what installation temperature is. Also if total movement of the run is more than the length of the expansion fitting then you need multiple expansion fittings in the run.
GoldDigger
Placerville, CA, USA
Retired PV System Designer
Which can cause some problems equalizing the motion over both expansion couplings unless you tie down the center point if the run.
Sent from my Pixel 4a using Tapatalk
GoldDigger
But the run doesn’t get longer - that’s what the expansion joint is for.
Picture a straight run between two fixed boxes. This distance between boxes never changes. As the conduit expands, the expansion joint “absorbs” the increase in pipe length!
Not true when one purpose for the expansion joint is to accommodate motion of one or both termination boxes.