If you don't like a website there is a way to avoid it.
I'd rather there were less veiled threats and alienation from sorts who's >>>>JOB<<<< it is to keep the peace here.
~RJ~
If you don't like a website there is a way to avoid it.
compared to the 1980s?
Lots of things cost more than they did in the '80s
So your answer is we should be able to run #16 to water heaters. :roll:Which we must ask, why is our trend to increase while everyone else decreases?
Of course, thats why any electrician regardless of the code at hand should be aware of voltage drop. Even with our conservative wire you can still get excessive voltage drop under the right conditions. Benefit is less cost, material and labor.
So your answer is we should be able to run #16 to water heaters. :roll:
Going to an ampacity table based on conditions of use will save copper in most installations. I know you may not agree, but other certainly would.
I'm all for saving money and reducing material cost. I often wire to code minimum. But what you propose is ridiculous.
Why is it ridiculous when it does just that?
Because it's not likely to ever be allowed by the NEC.
Because it's not likely to ever be allowed by the NEC.
They put AFCI's in the NEC
Of course if you had the money to back up your requested change you have a better chance of getting what you want.
Manufacturers have far too much influence over the NEC to ever allow ampacity requirements to be relaxed (read: less copper and aluminum for them to sell.)
Not sure you can really say that about the CEC, as there is an intent between CSA and NFPA to bring those codes much closer together. The change in a few of the values in the NEC ampacity tables a couple of code cycles ago, was part of that process.Except that the CEC and IEC are irrelevant to American wiring systems and are just as subjective as the NEC in many ways.
There are very limited actual requirements in the NEC for performance testing.Performance testing is an NEC requirement , So is an assured EGC program, there is no 'T&A allowed' , nor would a 'bang test' be advised at high amperages unless one has unlimited funds for equipment and ER visits
The particular meter or method w/meter is not detailed in the NEC, as it's assumed a competent electrician can operate and knows the limitations of more than a mere continuity check
One can either pursue the informational notes , or google this for a world of our trade rags offerings if not.
~RJ~
Assured EGC program is an alternative to GFCI protection in some instances though.There are very limited actual requirements in the NEC for performance testing.
There is no requirement to have an assured EGC program in the NEC.
Informational notes are just that...information...not requirements.
I'm all for saving money and reducing material cost. I often wire to code minimum. But what you propose is ridiculous.
Assured EGC program is an alternative to GFCI protection in some instances though.