I'm in Chicago, with the 2017 NEC with modifications. A commercial catering business, no other tenants in the building. I did the load calculation some time ago and came up with 800 amps, 120/240 volt 3 phase. The owner has asked me to bid both 800 amps and 1000. So I've come up with these 3 options. Please look over and see what I have wrong.
option 1) 800 amps
Table 310.15(B)(16) 75*C column
2-sets of 600 kcmil, 420 amps ech, = 840 amps.
Table C.1
2 sets of 4) 600 kcmil 3 1/2" IMC or RMC
250.66 & table 250.66
2 x 600 = 1200 kcmil = 3/0 in 1"EMT GEC to the water service
#6 in 1/2 EMT, to the ground rod
Option 2) 800 amps
Table 310.15(B)(16) 75*C column
3-sets of 300 kcmil, 285 amps ech, = 855 amps.
Table C.1
3 sets of 4) 300 kcmil 2 1/2" IMC or RMC
250.66 & table 250.66
3 x 300 = 900 kcmil = 2/0 in 1"EMT GEC to the water service
#6 in 1/2 EMT, to the ground rod
Option 3) 1000 amps
Table 310.15(B)(16) 75*C column
3-sets of 400 kcmil, 335 amps ech, = 1005.
Table C.1
3 sets of 4) 400 kcmil 3" IMC or RMC
250.66 & table 250.66
2 x 600 = 1200 kcmil = 3/0 in 1"EMT GEC to the water service
#6 in 1/2 EMT, to the ground rod
The picture is my line drawing.
Thanks
MIke
option 1) 800 amps
Table 310.15(B)(16) 75*C column
2-sets of 600 kcmil, 420 amps ech, = 840 amps.
Table C.1
2 sets of 4) 600 kcmil 3 1/2" IMC or RMC
250.66 & table 250.66
2 x 600 = 1200 kcmil = 3/0 in 1"EMT GEC to the water service
#6 in 1/2 EMT, to the ground rod
Option 2) 800 amps
Table 310.15(B)(16) 75*C column
3-sets of 300 kcmil, 285 amps ech, = 855 amps.
Table C.1
3 sets of 4) 300 kcmil 2 1/2" IMC or RMC
250.66 & table 250.66
3 x 300 = 900 kcmil = 2/0 in 1"EMT GEC to the water service
#6 in 1/2 EMT, to the ground rod
Option 3) 1000 amps
Table 310.15(B)(16) 75*C column
3-sets of 400 kcmil, 335 amps ech, = 1005.
Table C.1
3 sets of 4) 400 kcmil 3" IMC or RMC
250.66 & table 250.66
2 x 600 = 1200 kcmil = 3/0 in 1"EMT GEC to the water service
#6 in 1/2 EMT, to the ground rod
The picture is my line drawing.
Thanks
MIke