We can't use PVC here. Thanks though. I know you have to bond at both ends. A pain in the butt.Avoid the GEC in EMT. You will need to bond each end. PVC sch 40 or if needEd Sch 80 if need physical protection. Sch 80 is considered equal to RMC
We can't use PVC here. Thanks though. I know you have to bond at both ends. A pain in the butt.Avoid the GEC in EMT. You will need to bond each end. PVC sch 40 or if needEd Sch 80 if need physical protection. Sch 80 is considered equal to RMC
Thanks. That's why I thought of that plan. Somehow it kinda goes against my belief of everything should have over current protection.Since the Chicago 2018 Electrical Code is the 2017 NEC with lots of amendments, you can still do a MLO with 6 service disconnects and no main. The service entrance conductors will have to have an ampacity at least equal to the calculated load, but do not have to have an ampacity equal to the sum of the ratings of the six service OCPDs.
About three years ago I priced a 1000 amp panel board both with just 6 200A breakers (MLO) , and with the 6 200's plus the addition of the 1000 main breaker. It was just about double the price, $4500 vs $9000. I use MLO whenever I can, unfortunately, where I do all my commercial work is on the 2020 code now.I was going to save this question for another thread but since you made this comment.
what do you guys think about me just installing a six throw panel as the main? If you have more than six throws you need a main. The six throw panel saves all the money for an 800 or 1000 amp main. Those are expensive and then you would still have to use some kind of panel board to split it up.
Did they get rid of the six handle rule for 2020?About three years ago I priced a 1000 amp panel board both with just 6 200A breakers (MLO) , and with the 6 200's plus the addition of the 1000 main breaker. It was just about double the price, $4500 vs $9000. I use MLO whenever I can, unfortunately, where I do all my commercial work is on the 2020 code now.
If still on 2017 that is probably least cost method in many cases.I was going to save this question for another thread but since you made this comment.
what do you guys think about me just installing a six throw panel as the main? If you have more than six throws you need a main. The six throw panel saves all the money for an 800 or 1000 amp main. Those are expensive and then you would still have to use some kind of panel board to split it up.
No, but they can no longer be in same panelboard or same vertical section of a switchboard.Did they get rid of the six handle rule for 2020?
He is in Chicago, and if they do the future updates to their electrical code like they have been done in the past, it will be 20 years or so before they release a new version.If still on 2017 that is probably least cost method in many cases.
If on 2020, you can still have six mains but they can no longer be in one enclosure or same vertical section of a switchboard.
They just getting or recently gotten AFCI requirements then? Or since they require steel conduit for most part did they amend that out?He is in Chicago, and if they do the future updates to their electrical code like they have been done in the past, it will be 20 years or so before they release a new version.
So why would this be? it does not appear like there is any safety benefit to doing it this way.If on 2020, you can still have six mains but they can no longer be in one enclosure or same vertical section of a switchboard.
Exposure to energized line side busing.So why would this be? it does not appear like there is any safety benefit to doing it this way.
They added the following exception to 210.12.They just getting or recently gotten AFCI requirements then? Or since they require steel conduit for most part did they amend that out?
How are you ever exposed since the enclosure can't be open unless you have proven it is de-energized or you are wearing a moon suit (if needed) and rubber gloves.Exposure to energized line side busing.
Another ridiculous code change without substantiation and trying to make the NEC a design manual.How are you ever exposed since the enclosure can't be open unless you have proven it is de-energized or you are wearing a moon suit (if needed) and rubber gloves.
Ask NFPA, some of us don't necessarily like it either.How are you ever exposed since the enclosure can't be open unless you have proven it is de-energized or you are wearing a moon suit (if needed) and rubber gloves.
Does that mean there are no AFCI requirements in Chicago?Exception No. 1 to 210.12(A), (B), and (C): It shall be permitted to omit AFCI protection for that portion of the branch circuit enclosed in rigid metal conduit (RMC), intermediate metal conduit (IMC), electrical metal tubing (EMT), or Type MI cable sheath meeting the requirements of 250.118 along with metal outlet and junction boxes.
Sadly that’s true. We aligned with the 99 NEC in 2000 and the next one was 2017 in 2018. Before that we had our own crazy code.He is in Chicago, and if they do the future updates to their electrical code like they have been done in the past, it will be 20 years or so before they release a new version.
We got Arc faults in 2000 and in 18 everything has to be arc fault but they added the exception it we use conduit. Which I think is good.They just getting or recently gotten AFCI requirements then? Or since they require steel conduit for most part did they amend that out?