jwelectric
Senior Member
- Location
- North Carolina
LarryFine said:Maybe not, but one receptacle can satisfy both sections.
Although I once would have agreed, now I disagree with this thinking.
Explain what is meant by 210.52(B)(1) when it clearly refers to the two areas as being separate
(1) Receptacle Outlets Served. In the kitchen, pantry, breakfast room, dining room, or similar area of a dwelling unit, the two or more 20-ampere small-appliance branch circuits required by 210.11(C)(1) shall serve all wall and floor receptacle outlets covered by 210.52(A), all countertop outlets covered by 210.52(C), and receptacle outlets for refrigeration equipment.
Why not just make the rule read like this
(1) Receptacle Outlets Served. In the kitchen, pantry, breakfast room, dining room, or similar area of a dwelling unit, the two or more 20-ampere small-appliance branch circuits required by 210.11(C)(1) shall serve all receptacle outlets.
There is a reason why they describe the two areas as being different. Wonder why that is?