Greetings,
I am a 3rd year Apprentice in Seattle. My Journeyman and I were fortunate to landl the load side of a 30 kva transformer. Transformer was fed to a disconnect which was for a commercial space meter center.
Ok, the transformer was a Delta/Wye stepping 480 down to 120. Line side was identified with high voltage phasing... brown, orange, yellow. I felt that the load side should have been identified with the high leg marked as orange.
Well, this didn't pass with the Inspector and my Foreman and Journeyman gave me grief over this matter.
My question is simple: who was correct?
If I was wrong, can you explain why?
Where can I find it in the 2005 code book? 110.15 is Hi leg marking, 408.3 (e) is phase arrangement. I understand those rules. If it is stepping down the voltage wouldn't the load side measure accordingly on the meter?