Installing 1500 watt field lighting. Each pole (circuit) will consist of 4 lamps, each lamp ballast is 1700 va, with 240 volts applied.
The circuit load works out to 28.33 amps, (1700 x 4 /240). With the 125% factored in being 35.4 amps.
May be splitting hairs with the question, but does this get by with a 35 amp breaker or can it be a 40 amp?
Does anyoune make a HID breaker in a 35, (breaker will be "switch). Seen only 30 and 40 on SqD website.
I plan on stringing #6 Al to satisfy the voltage drop.
Thanks