Series rating are not "stackable". You cannot use the results from one series rating as the input to a different one.Can't use all QS because I have loads that are less than 100A
Might be a stupid idea but do you think I can have 800A Bussman JJN and JJS fuses in series and then it will series rate with both HQP and HQS breakers?