wwhitney
- Berkeley, CA
- Retired
Wanted to check my understanding:I've continued to gnaw at the idea of adding inductance to drop the fault current.
The only way to drop the fault current is to add impedance. One reason to add reactance rather than resistance is that if the load is power factor 1, then the voltage change at the load due to the extra reactance will not (to first order) occur as a drop in the magnitude of the voltage, but as a phase shift, so the load performance is not affected. Correspondingly, if the load power factor were say 1/sqrt(2) (45 degree power factor angle), then you'd want to add resistance and reactance (of opposite sign(*) to the load) in equal parts to achieve the same effect.
Is that right?
Cheers, Wayne
(*) I'm not sure if the convention is that inductance or capacitance causes positive reactance (I think it's inductance?) and if non-unit power factor loads are typically inductive or capacitive (I think inductive, since you hear of capacitors being used for PFC?)