Open delta is occasionally used around here for rather fixed loads where the major load is a single three phase motor or something similar.Open delta’s are generally used where the three phase load is small, and the majority of the load is single phase. The high leg is seldom used for single phase loads. This works well with utilities because the single phase load transformer is larger than the second transformer the high leg comes from. With a full delta, it overloads the one winding that the neutral taps from, that’s why the manufacturer limits the neutral to phase loads.
On occasion to supply three phase to a remote site where the primary distribution does not have all three phase conductors available. The POCO generally will want to use all three phase conductors if the needed kVA is over a certain level though. Do have a few existing installs that are higher capacity still out there but they wouldn't approve them today without all three phases if they were a new application for service.