Just use I-Line panels for everything, They have up to 600 volt rated breakers for them.AND a panel that will allow you to install one on the B phase...
This is an under rated aspect of the entre question rendering it, for the most part, moot. For 3 phase panels that are rated 240/120V or 208/120V, ALL of the single pole breakers are "slash rated", meaning they can ONLY be used where the L to G potential is 120V maximum. You CANNOT use slash rated breakers on a 208V to ground potential circuit. The only "straight 240V" rated breakers are 2 pole or 3 pole (and the 2 pole are more expensive than the 120/240V rated 2 pole breakers).
So if you were to WANT to use the B phase to N as a 208V single phase circuit, the only options would be:
So to be able to use that B phase to neutral, it will cost you MORE than what you might think in one way or another AND be risky for some future person who doesn't understand the ramifications and connects a 120V load to it.
- Use a 2 (or 3) pole straight rated breaker and only use one pole, (which is pointless, because you might as well use 240V and NOT use the neutral). This would ONLY make sense if you were somehow stuck with a motor that was rated for only 208V single phase. I have never seen one.
- Buy a 480/240V 3 phase panel and use the entire thing at 240V, which may be confusing to someone in the future. In some brands, you can mix breakers of different voltage ratings, but in reality, you are always buying a 480V rated panel, so it will be bigger and more expensive than an equivalent 240/120V one.
Not sure if there is 600 volt single pole breakers though, but definitely is 277 volt rated ones, guessing there likely is 347 volt rated single pole breakers though.