kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
I just don't see it being required to be any larger then max load served. In the OP's case max load served by the grounded conductor is just a few VA @ 120 volts. I would understand if they said no smaller then 250.122 requirements, but they don't mention it at all for branch circuits.I never understood why we don't have language in Art. 210 similar to 215.2(A)(2) for the cases where a piece of equipment needs a limited neutral for whatever reason. It would seem obvious that if this is done, as in the OPs case, that it needs to be a least as large as an EGC. But maybe you are right, it needs to be full sized except for the exceptions. But that seems crazy to me.
I have ran 14AWG neutral several times for such cases - 240 volt three phase motor - with 120 volt contactor for control-no separate control transformer. Usually on aeration fans for grain storage bins - many not listed units either:roll:. I would rather run the 14 AWG then tie the control to the EGC like I have seen many others do. In fact sometimes I need to lift the neutral conductor from a grounding lug in these non listed units