High Nuetral Current, no nuetrals connected

Status
Not open for further replies.

iwire

Moderator
Staff member
Location
Massachusetts
that's all I'm asking for
what are the basic measurements: line i's and N i
line 1 - line 2 = N
could give us a starting point or a direction to start looking

if line 1 = line 2 and N ne 0 wouldn't that tell us something?

Sorry I even said anything, I should know better than that.
 

Ingenieur

Senior Member
Location
Earth
Sorry I even said anything, I should know better than that.

I make a general observation directed to no one
we need basic i measurements

you comment it's meaningless
I respond it could give us some direction
you play snarky martyr
why?

how about
a logical response sans emotion why knowing the current(s) is moot
Or ignore

if you were troubleshooting what would be one of the first steps?
measure the currents?
 

templdl

Senior Member
Location
Wisconsin
The equipment is straight 208 volt, no neutral. No neutral no neutral current right?

Agree. My thought was at the transformer itself where a K- factor Transformer has a 200% neutral. But, a neutral extended along with the phase conductors where there are no L-N loads, nothing connected to it, there shouldn't be an current, agreed.
 