ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
At a plant where electrical distribution system was installed ~ 1980. They did not run wire equipment grounding conductors with feeders from the 4160V/480V transformers to 480V MCCs.
"Assured" Bonding strarts with 250.92(B).
Mike Holt wrote about it here

Bonding bushing flowchart attached
 

Attachments

  • bonding bushing flowchart.jpg
    bonding bushing flowchart.jpg
    123.6 KB · Views: 16

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
And your 'prefect' ground conductors DO normally carry current? :oops:


Exactly what I was thinking... A piece of emt has less impedence then a copper conductor sized for the circuit. That being said we always ran a grounding conductor also known as an equipment grounding conductor.
 

kwired

Electron manager
Location
NE Nebraska
I've seen far more ungrounded and grounded conductor failures than I have metal raceway as grounding conductor failures.
Outside of a poor install, same here.

Run into many 60's thru 80's installs of EMT that wasn't properly supported, or just poor routing selection also contributes, especially in attics and over time you get broken fittings (particiularly die cast fittings) from people that have been working in that attic.
 

kwired

Electron manager
Location
NE Nebraska
Right, however a wire EGC differs in no way from a wire carrying load current.
For instances that need a 8 AWG EGC or larger, I think are typically made up pretty well, and maybe are somewhat bullet proof.

Raceways or even non metallic wiring methods containing 14 or 12 AWG EGC's, I think you run into higher chance of a bad connection. Unlike the ungrounded conductors, it will never be known majority of the time. But with a metallic wiring method you also have a certain amount of redundancy even if someone forgets to tighten a set screw or compression nut on occasion.
 

480sparky

Senior Member
Location
Iowegia
We're saying a grounding conductor, for the purpose, functions the same as using a metal raceway for the purpose of providing an ECG. Both are accepted by the NEC. Both function as designed... if installed correctly. Do sloppy work, and either can fail. Have a wire slip out of a wire nut when you shove it in the box? Installer error. Forget to tighten a set-screw on a connector? Installer error.

In terms of ability, the metal raceway far exceeds the capacity of any wire it can contain for fault clearing.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
For instances that need a 8 AWG EGC or larger, I think are typically made up pretty well, and maybe are somewhat bullet proof.

Raceways or even non metallic wiring methods containing 14 or 12 AWG EGC's, I think you run into higher chance of a bad connection. Unlike the ungrounded conductors, it will never be known majority of the time. But with a metallic wiring method you also have a certain amount of redundancy even if someone forgets to tighten a set screw or compression nut on occasion.


Of course, but if a particular conductor, splice, or termination is of poor design or formulation you find out about it on current carrying via joule heating. Copper, wire nuts, wagos, lever nuts, screw terminals ect have all evolved around carrying current continuously.
 

kwired

Electron manager
Location
NE Nebraska
We don't know that because they do not carry current, or is there something similar like Fe current carrying conductors to test that concept.
Fe carries current fine, not as good as same cross section area of copper, but a raceway will almost always have more current carrying ability than the minimum required EGC that would be pulled through it. The problem is going to be quality of connections for both the raceway and the copper conductor. Installers can make a mistake with either.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
We're saying a grounding conductor, for the purpose, functions the same as using a metal raceway for the purpose of providing an ECG. Both are accepted by the NEC. Both function as designed... if installed correctly. Do sloppy work, and either can fail. Have a wire slip out of a wire nut when you shove it in the box? Installer error. Forget to tighten a set-screw on a connector? Installer error.

In terms of ability, the metal raceway far exceeds the capacity of any wire it can contain for fault clearing.


Sure. But how do we know correctly installed conduit has the same impedance over time vs when new? How do we know the steal doesn't oxide?
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Fe carries current fine, not as good as same cross section area of copper, but a raceway will almost always have more current carrying ability than the minimum required EGC that would be pulled through it. The problem is going to be quality of connections for both the raceway and the copper conductor. Installers can make a mistake with either.


Of course. Fe carries current just fine as well as 4000 series aluminum. However, would you wire a home with 4000 series aluminum?

Just making a comparison, don't mean to come across as a hard head answering your questions/statments with questions :)
 