Tom227 said:the holes are 7/8" and they are about 2" center to center and there are about 10 holes in the joists
This is a structural issue...and your inspector is correct. You are pretty much screwed. See Section 502.8.1 of the IRC
ceknight said:Tom227 said:the holes are 7/8" and they are about 2" center to center and there are about 10 holes in the joists
If this is traditional lumber, and the holes are drilled in the middle of the beam, I cannot see how this is a framing violation. Maybe you drilled too low along the bottom portion of the beam.
inspector23 said:If you are indeed held responsible for replacing the members in question, perhaps you could have a licensed structural engineer provide a fix for the materials involved that would not require removing the damaged ones and replacing them with new ones.
No, the engineer might not be cheap, but it might be worth exploring to see if all the costs involved would be cost beneficial for you as an alternative to replacing everything.
In cases I have experienced, the AHJ will accept a licensed, approved engineer report that is wet signed ( not a fax or a copy) so long as it initially details the existing problem and provides clear, concise instructions for re-establishing the structural integrity.
just a thought .........
Pierre, from your next post:Pierre said:If this is traditional lumber, and the holes are drilled in the middle of the beam, I cannot see how this is a framing violation. Maybe you drilled too low along the bottom portion of the beam.
I don't know if you were correcting yourself or maybe missed it when you posted it. Just throwing that up there for clarity's sake.R508.2.1 Sawn lumber.
The diameter of holes bored or cut into members shall not exceed one-third the depth of the member. Holes shall not be closer than 2 inches to the top or bottom of the member, or to any other hole located in the member.
Tom227 said:the holes are 7/8" and they are about 2" center to center and there are about 10 holes in the joists
If the inpsector is a professional, and you approach situations as "out of sight-out of mind", I fear you will have a long bumpy ride in his area.They are in the crawlspace and I hope he doesn't see them.
allenwayne said:Tisk,Tisk,Tisk :wink: Out of sight out of mind right :wink: One thing amazes me.We as electricians are also supposed to be engineers.
jeff43222 said:Although I have never run into this kind of situation myself, I find it interesting to contemplate. The licensing exam I took dealt strictly with the NEC and electrical theory. While I'm not disputing the IRC rules, I've never even seen a copy of them. Seems to me that if we're responsible for following IRC rules, the licensing exam that electricians have to take should at least make a mention of it.