Hameedulla-Ekhlas
- AFG
Good question,
you have 8kW generator please check the power factor which is very important to find the generator kVA.
if the power factor is 0.8 then you have 10kVA generator with 0.8 power factor.
It means you might have the following generator description, if the power factor is 0.8
10kVA
8kW
6kVAR
0.8 power factor
on load side you have 30ampere with 240 volt 1ph,
load Apparant Power (S) = I * V = 30*240 = 7.2kVA
According to genertor 10kVA, 8kW, 6kVAR ,0.8 power factor
there will be no problem for this generator even this generator works at its 80% of its maximium load
10kVA
8kW
6kVAR
0.8 power factor