What I can't get my head round is why you would need almost 100 kVA for a residence.I like to tell people, phase A 200a, phase B 200a, so you have 400a .
I like to tell people, phase A 200a, phase B 200a, so you have 400a .
What I can't get my head round is why you would need almost 100 kVA for a residence.
It looks like this is the source of the calculation done by the homeowner:
https://www.hunker.com/12285752/how-to-calculate-a-breaker-panel-load
I'm tempted to write to their editorial team, and ask how much they would pay for a _correct_ calculation
-Jon
How do you respond when this math is on DIY internet?
Thanks,
Mike
The home had passed all inspections, the meter was installed and had received the cities final.
It looks like this is the source of the calculation done by the homeowner:
https://www.hunker.com/12285752/how-to-calculate-a-breaker-panel-load
I'm tempted to write to their editorial team, and ask how much they would pay for a _correct_ calculation
-Jon
This is the calculation I received from a homeowner. The house is roughly 3000 S.F single family with attached garage. Gas heat, Gas water heater (tankless), Gas cooking. How do you respond when this math is on DIY internet?
Thanks,
Mike
I once saw an electrician tell an owner that his 225A panel was overloaded because it had forty two 20A circuit breaker...42*20=840A.
Pretty much the theme of this thread.
My good golly gosh!
What kind of dwelling needs a 600A supply??
Most dwellings don't need that capacity. Occasional large ones do. I had one with 60 kW of electric heat plus two laundry rooms, 5 4.5 kW water heaters, and then 10,000+ square feet of space with otherwise relatively normal loads. Can't remember if POCO set a 75 or a 100 kVA transformer. I ran 4 sets of 200 amp conductor to 4 200 amp service disconnects on that one, was better design choice as it was less cost on gear but maybe extra conductor made up that difference, plus left more future capacity if ever needed than putting on a single 400 amp main which would have been enough from recollection but wouldn't have had much room for additions.What I can't get my head round is why you would need almost 100 kVA for a residence.
And I like to strongly discourage such statements. With 200 amps on phase A and 200 amps on phase B, you have a "total" of 200 amps. For the moment let us assume that the loads are balanced. Current that leaves the panel on phase A will return to the panel on phase B. It is the same current.I like to tell people, phase A 200a, phase B 200a, so you have 400a .
His claim is based on a meaningless collection of data. The service is not undersized, there is no code violation, and there is no safety hazard. If he wants a 320 amp service, give him a cost proposal for the upgrade. You own them nothing.His claim was the service was grossly undersized, an obvious code violation, and safety hazard. He requested a 320Amp service be wired and installed at no charge to correct this obvious error.
His claim is based on a meaningless collection of data. The service is not undersized, there is no code violation, and there is no safety hazard. If he wants a 320 amp service, give him a cost proposal for the upgrade. You own them nothing.
How many 3000 square foot houses have 200 amp services. Many.
Plus, it has Gas, which makes this even more obvious that you count on this service as fine.
You can only put so much crap in a 3000 square house and have it turned on at the same time.
One solution, change all the breakers to 15 amp!
To change breakers to 15 amps doesn't change anything in a load calculation. General lighting load is calculated at 3 VA pr sq ft . Small appliance circuit at 1500 VA each.
AC load at FLA on name plate and not breaker size.
You can put lots of things in a 3000 sq ft house that will cause the load to go way up.
Tankless electric water heater.
Heat pump with electric heat strip back up or even worse a big electric furnace.
Couple of of the big tesla car chargers
hot tub or pool heater (if electric)
What I'm getting at is the size of the house has less to do with the service load than major appliance loads.
If they think $5k a month is too much, then they will quibble if the energy bill doesn't decrease after upgrading the service/equipmentOf course, if they really are using $5000 worth of electricity each month, then they shouldn't quibble about paying a few K for an upgraded service
(If the DIY calculation was correct, then they would be using some 72kW, at 24 hours per day 30 days a month, it adds up pretty quick ....
-Jon
Sure it does put that heat pump on a 15 amp breaker instead of a 40 and the load will only run for a little while before it is automatically reduced by a tripping breakerTo change breakers to 15 amps doesn't change anything in a load calculation. General lighting load is calculated at 3 VA pr sq ft . Small appliance circuit at 1500 VA each.
AC load at FLA on name plate and not breaker size.
You can put lots of things in a 3000 sq ft house that will cause the load to go way up.
Tankless electric water heater.
Heat pump with electric heat strip back up or even worse a big electric furnace.
Couple of of the big tesla car chargers
hot tub or pool heater (if electric)
What I'm getting at is the size of the house has less to do with the service load than major appliance loads.