Originally posted by paul:
Can't tell for sure, but is that URD inside building lines?
That yellow stripe is the giveaway that it's URD. Some (maybe all) of the URD that I've installed lately is dual rated as XHHW.

I hate to see so much raggedy romex insulation inside the panel, but that's a workmanship issue.

This appears to be main panel, and not a subpanel, so I'm not sure why the special effort was made to seperate the grounds and neutrals. It makes for a messy panel with the grounds and neutrals criss-crossing the panel to get to their respective bars.

I note the missing bushing on the PVC conduit.
 
Re: home owner permit

Why was the photographer lying on the floor?
Because he was laughing his a*** off :D

In this photo with the angle of it , I think dave was wanting us to note the amout of NM in each NM connector but also I see where there are a few doubled up neutrals and neutral with EGC's on the neutral bar. There are some panels that do require seperate EGC bar as there is not enough terminals on the neutral bar following 408.20

Is there a main bonding jumper? Can't tell
 
Re: home owner permit

I don't see anything wrong about running the grounds and neutrals to separate bars. It is not necessary but it is not wrong either.

It is messy looking but not a lot worse than a lot of stuff I see in industrial facilities after equipment has been there a few years.

Might be some issues that are not obvious to me (other than the ones already pointed out), but it seems to me that neatness counts, but not all that much. When the cover is on, no one will see it anyway.

The real question in my mind when I see something made up like this is whether it is safe or not. That counts more than neatness to me.

<added> by the way - what is URD?

[ November 07, 2005, 09:51 AM: Message edited by: petersonra ]
 
Re: home owner permit

Originally posted by petersonra:


<added> by the way - what is URD?
I believe "URD" is a nickname for USE translating to Underground Residential Development stemming from poco terminology. AKA triplex.
 
Re: home owner permit

I think it's somewhat messy but I've seen worse from professionals. The NM's per connector I think Dave's gonna tag. But aside from that it doesn't look all that bad for a home owner installation. Bob mentions "whether it's safe", it looks like it is to me.

It does kinda illustrate how non electrical professionals just don't know how everything should be done even though they probably think they know how to do it.

Edit: Error B.

[ November 07, 2005, 11:13 PM: Message edited by: Physis 2 ]
 
Re: home owner permit

Unless manufacturers have changed the listing there are way to many pieces of NM in the connectors.It my eyes aren`t decieving me there is an unused connector on the left side of the panel.
As a foot note I also split my grounds and neutrals on seperate bars but not in an abortion like that a few well placed 8 in. tie wraps can make a really neat job ;)
If any of my guys tried to get away with cr_p like that ,it`s off to D.T.R.E .Did anyone see the 10/3 sheathing,looks like it is within the connector itself and not with the enclosure.
 
Re: home owner permit

By Jim: If any of my men did work like this i would send them to McDonalds.Not for a treat but to return to there old job .
Jim Do you hire many from there? :D

The two neutrals per terminal would be a red tag also. 408.21

Counting the neutral terminals down from the top, terminals 1, 6, 8, 10, 11 have more than one wire under a screw.
 
Re: home owner permit

The panel is mounted 4" too high and it is a tall panel to begin with!
Also, there is a main disconnect at the meter mounted on the side of the house.
Plus there is at least one violation no one has mentioned yet......

Check the photo below for the manufacturer's labeling instructions for the connectors.
I have always allowed two 12/2 or 14/2 per connector but only one 12/3 or 14/3. For 10/3 it is usually a 3/4 connector.

con1.jpg
 
Re: home owner permit

Arlington's 3/8" romex connectors allow up to 3 of certain cables. They have a very comprehensive chart of cable combinations here: http://www.aifittings.com/c_19.htm

Their normal 3/8" locknut type connector is the model 840 on the chart.

I forget what the old style connectors were called that were like an aluminium sleeve that you smashed with your nine's were called. They allowed 3, 12-2's.

[ November 07, 2005, 09:05 PM: Message edited by: mdshunk ]
 
Re: home owner permit

Actually the 841 is comparable to the above post and yes they allow 3 14/2 NM in them and many other combos.

Arlington NM CABLE CONNECTORS

Click on the Click here in Click here for complete cable ranges.

I wonder how Arlington can get it's connectors listed for more and Raco only allows one cable?

For those of you who want a place to go to all the Electrical Manufacturers who have web sites go here Electric Find.com

And don't forget to save it in your favorites or book marks.
 
Re: home owner permit

OK, a few minor violations. Nothing shown is going to burst into flames or shock anyone. As others have said, I've seen much worse done by so-called "professionals."
 