That would be 200W.
That would be 200W.
I know what you are getting at. But it's more correctly inductive reactance and capacitice reactance you want to match and (nearly) cancel. The reactance depends on supply frequency rather than the natural LC resonance frequency. In fact, natural resonance is best avoided in most cases.
I measured this current waveform a couple of weeks ago:
![]()
The fundamental is 50 Hz (UK) but clearly there is a whole bundle of other frequencies mixed in.
Not good.
One thing i see is if you leave PF alone or increase your now bad PF your watt meter will actually read less wattage so your cheating the local power company maybe this why one box does fit all ?
Well Gar we kinda were thinking not improving but making it worst meaning adding more capacitance into the circuit then needed meaning adding more to see how it would effect the wattmeter ?090511-1906 EST
ohmhead:
You statement is incorrect. A residential watt-hour meter measures the cumulative energy you use from one reading to the next. Energy is work done. Work is raising a weight, using friction to generate heat, running a fan to move air, heating a resistor, etc. This work is what the watt-hour meter measures.
If you have a motor with a bad power factor doing some work. For example: no external load on the motor, but thru bearing friction and windage work is being done. This motor will have a low power factor because it is not doing much work in comparison with its capability. Thus, the inductive excitation current is large compared to the resistive component. The resistive component is a result of the work being done.
Add power factor correction, a capacitor, this will reduce the reactive current as seen looking at the motor and capacitor combination. It has no effect on the resistive component. The resistive component does not change if the voltage, frequency, and load do not change.
An ideal watt-hour meter only uses the resistive component in combination with the voltage to determine energy usage. Improving the power factor does not cheat the power company,
Read thru this whole thread again and see if this has not been said many times.
The post where I provided experimental data with a lamp and capacitor showed that a large change in power factor had no effect on the power reading. The slight increase in power with the capacitor connected was from resistive losses in the capacitor.
.
Residential customers throughout North America could see a realized savings of 8% - 10% typically and as much as 25% on their electrical usage (and thus power bills). The Power-Save 1200? is UL Certified as the Cat. No. ABET 2201 and CSA certified.
The Video at Power Save clearly does not adhere to trust and truth as related to power saving.Advertise Honestly
Adhere to established standards of advertising and selling.
Tell the Truth
Honestly represent products and services, including clear and adequate disclosures of all material terms.
UL Tested and Listed
K8MHz thanks for your offer.
1.1 The requirements in Part i of this Standard apply to enclosed capacitors with integral protection intended to reduce the risk of rupture and venting of the capacitor enclosure under internal fault conditions.
http://www.bbbonline.org/reliability/requirement_small.aspI have no idea what Reliability Program means.
Interestingly although no mention is made of it, the instrument being used also displays power. It is the top reading.090512-0844 EST
In doing a Google search I encountered the following:
http://www.power-save1200.com/1200.html
From 1.99 KVA and 16.3 A of the first line I get 122.1 V. This is reasonable. From 1.99 and 1.43 I calculate 1.38 KVAR. Not a good correlation with 1.29 . My calculated PF is 0.719 .A/C just one leg
L1 , 16.3A , 1.43KW ,1.99KVA , Pf 0.75 lag , 1.29 KVAR no PS1200
L1 , 13.65A , 1.62KW ,1.65 KVA , Pf0.97 lag , 0.36 KVAR with PS1200
has an error in the PF. It should be about 0.101 . My calculation for voltage is 121.2 V. This indicates 80 W of power dissipation within the two capacitors or 40 W within 1. Without looking back I believe with the PS1200 only that the TED power reading was 100 W. TED and this instrument would correlate.PS1200 box. L1 - L2 , 6.52A , 0.08KW , 0.79KVAR , Pf 0.98 lead.
Re-arranging:Test load, two blowers , flood light, heater with fan. Red with PS1200
L1 , 4.61A , 0.6KW , Pf 0.98 lag , 0.11 KVAR
L2 , 12.8A , 1.52KW , Pf0.99 lag , 0.17KVAR
L1 , 7.7A , 0.69KW , Pf 0.69 lead , 0.7 KVAR
L2 , 13.9A , 1.55KW , Pf 0.91 lead , 0.7 KVAR
Is time taken into account? Is it possible the run time of the A/C system changes so it has to run longer to achieve the same amount of cooling?Another test today. A/C system , 3 Ton split ,cooling mode,motor load.
20 rotation of the disk , measured in seconds. red with PS1200
184 - 174 , 185 - 175 , 185 - 175 , 184 - 174.
That's it. I guess it would be pointless to deny that this device can reduce the electric bill.