some test results.
some test results.
Here is what I did today.
Setup is the same. Ted 1001 installed. Clamp ons on service entrance conductors before main breakers , transmitter on 20A dedicated single pole , Power Saver1200 on double pole dedicated 20A.
First step: All branch circuit breakers are off except Ted. Reading is 0.000
TED is working properly.
2nd :I turn PS1200 breaker on. Ted shows 100 Watt load, but the meter outside does not turn.
Amp reading on PS1200 wires , both 6.25A
Looks like PS pumping some reactive power back to the source.
3rd. Oven test. PS 1200 is off , I turn the oven on.
Ted reads 3.870 KW load ,steady.
I turn PS1200 on.
Ted reads 3.780 KW steady.
This is a nearly 100% resistance load, reading is 90W less!
4th step. Mixed load , single phase, my heat gun.
Oven is off , PS1200 is off, heat gun plugged in,
transmitter -heat gun on the same leg.
Ted reads 1350 watt.
Ps1200 is on
Ted reads 1260 watt.
5th step. Mostly inductive , motor load. Split A/C , 3ton. 240V
All other breakers are off. A/C in cooling mode.
A/H , compressor is running, without PS1200
Ted reads 3700 watt
I turn PS1200 on Ted reads 3600 watt.
That's what I've got. I know very well that there are other factors ,accuracy,
all sort of errors. I'd like to point out that we are Compering Data in this case.
Accuracy is more or less irrelevant.
The results are consistent. Dan
some test results.
Here is what I did today.
Setup is the same. Ted 1001 installed. Clamp ons on service entrance conductors before main breakers , transmitter on 20A dedicated single pole , Power Saver1200 on double pole dedicated 20A.
First step: All branch circuit breakers are off except Ted. Reading is 0.000
TED is working properly.
2nd :I turn PS1200 breaker on. Ted shows 100 Watt load, but the meter outside does not turn.
Amp reading on PS1200 wires , both 6.25A
Looks like PS pumping some reactive power back to the source.
3rd. Oven test. PS 1200 is off , I turn the oven on.
Ted reads 3.870 KW load ,steady.
I turn PS1200 on.
Ted reads 3.780 KW steady.
This is a nearly 100% resistance load, reading is 90W less!
4th step. Mixed load , single phase, my heat gun.
Oven is off , PS1200 is off, heat gun plugged in,
transmitter -heat gun on the same leg.
Ted reads 1350 watt.
Ps1200 is on
Ted reads 1260 watt.
5th step. Mostly inductive , motor load. Split A/C , 3ton. 240V
All other breakers are off. A/C in cooling mode.
A/H , compressor is running, without PS1200
Ted reads 3700 watt
I turn PS1200 on Ted reads 3600 watt.
That's what I've got. I know very well that there are other factors ,accuracy,
all sort of errors. I'd like to point out that we are Compering Data in this case.
Accuracy is more or less irrelevant.
The results are consistent. Dan