Homeruns entering panel from trough

This entire concept is dumb. Why not require the conductors in NM cable to be marked? Many MC cables already use conductors with surface markings.
Yeah this is one of those annoying things that can the NEC PLEASE just settle? Either require the inners to be marked THHN or have some statement saying something like " inner conductors of cable wiring methods shall be considered an approved wiring method when installed in conduit".
 
Yeah this is one of those annoying things that can the NEC PLEASE just settle? Either require the inners to be marked THHN or have some statement saying something like " inner conductors of cable wiring methods shall be considered an approved wiring method when installed in conduit".
Yeah this one is dumber than dumb. The NEC requires the conductors to be rated for 90°C but not marked as THHN or some other insulation type. Why?
 
Yeah this is one of those annoying things that can the NEC PLEASE just settle? Either require the inners to be marked THHN or have some statement saying something like " inner conductors of cable wiring methods shall be considered an approved wiring method when installed in conduit".
It won't happen. A Southwire engineer told me that the conductors in Romex are THHN/THWN today, but because there's no product standard stating what they're supposed to be they could be anything. And because of that you can't assume that the conductors are any specific type. Even though it's obvious by looking at them that they are THHN/THWN.
 
A Southwire engineer told me that the conductors in Romex are THHN/THWN today, but because there's no product standard stating what they're supposed to be they could be anything.
That's real good. If they can't even mark the conductors with what they are to make our jobs easier, another reason not to use NM.

-Hal
 
It won't happen. A Southwire engineer told me that the conductors in Romex are THHN/THWN today, but because there's no product standard stating what they're supposed to be they could be anything. And because of that you can't assume that the conductors are any specific type. Even though it's obvious by looking at them that they are THHN/THWN.
I'm usually not a fan of this, but the NEC could force a change in the product standard, all they have to do is put it in the NEC under construction specifications.

I remember seeing the product standard and it gives several options for the conductor insulation. One is THHN, but another option is some weasel word like "meeting the same specifications as THHN" 🤬
 
I remember seeing the product standard and it gives several options for the conductor insulation. One is THHN, but another option is some weasel word like "meeting the same specifications as THHN" 🤬
That should include being able to use it wherever you can use THHN.
 
I'm good with them marking it THHN.
I'm not good with them marking it THWN or THWN-2.

That may leed to use in wet locations.
It won't happen. A Southwire engineer told me that the conductors in Romex are THHN/THWN today, but because there's no product standard stating what they're supposed to be they could be anything. And because of that you can't assume that the conductors are any specific type. Even though it's obvious by looking at them that they are THHN/THWN.
Maybe easier for mfg not to mark it at all.

I do like the idea of an exception. When installed in a raceway.

Cleaner and easier as well less conductors in the raceway nipple for the op application.

It also reduces the amount of the conductor cross for derate if a single EGC ran from panel to a EGC bar or connection in the wire way.
 
I would have stripped off the jackets installed an EG bar or two in the gutter with one EGC on down and never been called on the conductors not being correct. As suggested YMMV.
What I generally have done as well, though as mentioned the conductors in NM cable are not marked and technically not allowed to be run as individual conductors in raceways. Never have had any inspector turn this particular type of thing down though.

That said, I have done this more often with MC cable than with NM cable and many MC cables do have marked individual conductors within.
 
Also make sure that your cables are arranged so that you do not nave more than 30 CCC's at any cross section. With 40 CCC's (20*2) derating would force you to come up with a different installation.
With only one nipple to the panel, they all will converge at that one point. I usually have done two or even three nipples which helps with this issue.
 
I really wish Siemens sold a can for thos panels that has no KO's
I don't think anybody has a "load center" with no KO's other than top wall of 3R types. Commercial/industrial panelboard cabinets can have that option. IIRC Square D usually comes standard with KO's on one end and a blank end on the other, though you probably can customize it to have either on both ends. IIRC their ends do bolt on and could be easily changed in the field as well. I've used more outdoor panels than indoor ones, I know the bottom of those are removeable Had one time in past where strong winds caused major damage at one installation. Replaced existing panel with a new one, but kept the existing bottom end panel instead of measuring out and drilling/punching out same holes in same locations again.
 
My opinion is that each point on the circuit between enclosures has a well defined wiring method which should be determinable locally, just by looking at a cross section of installation. If that cross-section is conduit and individual conductors, no cable jacket, it's not a cable wiring method at that point.
I would suggest to electricians that if you see unmarked 'THHN' like wire in a panel or terminataoin point just assume its a 60C conductor for dry locations only.
The larger NM conductors 8AWG and up don't even resemble THHN they have a different stranding and are easy to identify.

when using 334.15(B) and another wiring method to serve as protection from physical damage I don't think there is anything under 334 or the NEC that requires the sheath to stay on for it to be a 'cable' still.
I mean what could the issue be? dielectric breakdown?
I suppose you could have a office in a industrial plant wired with NM.
Then some NM could share a wireway with a 600V circuit.
For anyone really concerned about dielectric NM cable is actually rated 600V and 334.116 states the sheath is for flame retardant and moisture resistance.
 
Last edited:
I don't think anybody has a "load center" with no KO's other than top wall of 3R types. Commercial/industrial panelboard cabinets can have that option.
Yeah I often order that NO KO option in a panelboard, more oftne than not, and if they had it for residential I would often order it also.
Just a hint hint to all the Eaton, SQD and Siemens reps on here LOL :)
 