kwired
Electron manager
- NE Nebraska
- EC
When it comes to ampacity adjustments, NM-B which is only type of NM that has been made since about 1987ish, is 90C conductor.I would suggest to electricians that if you see unmarked 'THHN' like wire in a panel just assume its a 60C conductor for dry locations only, the larger conductors 8AWG and up don't even resemble THHN they have a different stranding and are easy to identify.
Larger conductors are 7 strand instead of 19 strand, though I have seen 7 strand 'THHN' before. Kind of sucks to handle if it is say 4 -1 AWG, and you may not see much of of it. You used to see more 7 strand in those size ranges back when they were still commonly making type THW and maybe the earlier years of when THHN became the norm.
I still see 7 strand copper in irrigation cable for 10 AWG conductors quite often. Still better than solid by a long shot. Not sure if I like it better than 19 strand or not. Strands don't fray as easily, but are more of a pain to straighten out if they do get frayed.