M. D.
Senior Member
RUWired said:MD, I was asking of the hard wired requirement not needing protection.
http://ecmweb.com/mag/electric_stumped_code_28/
Q. Is GFCI protection required for a pool pump motor circuit?
A. GFCI protection is not required for hardwired circuits that supply pool pump motors. However, receptacles rated 15A or 20A, single phase, that supply cord-connected pool pump motors must be GFCI protected [680.22(A)(5)].
Note: The outlet that supplies a self-contained indoor spa or hot tub, a packaged spa or hot tub equipment assembly, or a field-assembled spa or hot tub must be GFCI protected [680.44]. Because this rule applies to all outlets and not just receptacle outlets, the wiring for a hardwired self-contained indoor spa or hot tub, a packaged spa, or hot tub equipment assembly would require GFCI protection.
I can't find where it is required if it is hardwired.