I am only seeing 40 amp minimum in those instructions, no maximim.

As I mentioned earlier though, I'd probably put a 40 amp standard breaker at the house panel and use a 50 amp spa panel as the local disconnect.
 
I took this straight from the owner's manual that the PDF link was in from the Cocso link.

230V Wiring Instructions:
4 wires/Minimum 50 amp GFCI
Breaker #8 AWG 75°C Copper Wire
Minimum (less than 100’ length)

I still say 50A is correct.
 
Yea the manual says 40amp min but if you go back to the first page where i posted the picture the nameplate says 40 amp maximum.
But it doesn't say exactly what that 40 amps is. Is it maximum connected load, maximum load that will ever be able to run at one time, does it include any continuous loading factors? With HVAC equipment MCA does factor in 125% of largest motor, hot tubs don't seem to have any standards in which to follow.

If there is 40 amps of continuous load then NEC wants us to take that times 1.25 and you need a 50 amp circuit, again it don't tell us what that 40 amps is. If it gave us ratings of heaters and pumps utilized we could at least calculate something.
 
All it says is 40amps max. Im going to play it safe and feed the disconnect with a 40amp breaker. Worst comes to worst i can replace the 40amp with a 50amp and be good.
 
Check post #8. That is the picture i took of the nameplate.

Well the spec sheet I read is for the same model and it says 50A. I've probably put in close to 100 hot tubs and never saw one that required less than 50A.
I would also say a 40A GFCI would cost more than a 50A but it's your install.
 
Going to feed a 50 amp Gfi disconnect with a 40amp main to cover my bases. If it has issues and needs more power ill just throw in a 50 to replace the 40.
 