I then rescinded when I stated--"Good Point"
I think we're both thinking the same thing and it's making us both look like neither one of us makes any sense.
JAP>
Secondly look at the definition of "Switching Device "
No GFCI protectionWhere is the violation?
No GFCI protection
Circuit Breaker. A switching device capable of making, carrying, and interrupting currents under normal circuit conditions, and also of making, carrying for a specified time, and interrupting currents under specified abnormal circuit conditions, such as those of short circuit.
I'm not sure what you mean
I thought a circuit breaker was a form of a switching devise
Yes, for 120V appliances, but not 240V.You don't know that. I have seen these tubs come with a cord and plug that has a built in gfci
How do you know this is not a 120V tub and how do you know there is no gfci protection. I agree there does not seem to be one in the panel but it seems you know something I am missingYes, for 120V appliances, but not 240V.
Connecticut Winters, in a basement, next to a window, would need a 240v heating element, unless the occupant likes taking dips in ice ponds while enebriated, like they do in Finland.How do you know this is not a 120V tub and how do you know there is no gfci protection. I agree there does not seem to be one in the panel but it seems you know something I am missing
If the NEC does not want a disconnect closer than 5' then why do you think a panel would be allowed???. Let's not over think this.
I don't see a problem, it's empty, move it, have it moved, or go home. I don't care in some cases if it is technically legal.
Pulling out in front of a speeding truck because you have the legal right of way is not a good decision.
In this case the disconnect is in the panel. I am not arguing the panel being there but rather the disco.Regardless of what we may feel the NEC wants we have to go by what is written.
I don't see a prohibition for panelboards and OCPDs.
You just don't get to decide which one is the disco
I don't see a safety issue.
Standing in the (full) tub working on the panel is the equivalent of pulling out in traffic without space.
In other words personal responsibility should come into play.
Did you know you copied that from the section " Over 600 volts"
I like how so many people take items out of context. I also wonder why the CMP just did not use common words like disconnect, circuit breaker, switches.
My take is that this definition pertains to over 600 volts. therefore did not apply to things other than that.
So in my Humble opinion I feel that maybe at the time this "might" have complied.
CMP needs to stop creating confusion and be simple. Say just what they mean.
I have a 120 volt spa located outdoors, it keeps up the temp just fine in winter months around here - with the cover on the spa. It will not heat while pump is in user mode (high speed) because that would draw too much current for the supply circuit, but I am not going to be using the thing if it is really nasty cold out either. I realize winter may be nasty in Connecticut, but sure hope it is much warmer in that basement then it is outside.Connecticut Winters, in a basement, next to a window, would need a 240v heating element, unless the occupant likes taking dips in ice ponds while enebriated, like they do in Finland.
Since the fuse box is so close, I doubt a separate SPA disconnect --with GFCI reset-- is used.
You and jap had been discussing locating the disconnecting means remotely but leaving the panel in place.
In my opinion that would not be prohibited.
In my opinion we would get to do exactly that.
Thank you for pointing that out it was a quick search on the term switching devise. I went back and re=looked and did not find a definition for the term “switching device.”
In my opinion any breaker marked SWD would be considered a switching device
Device. A unit of an electrical system that carries or controls electric energy as its principal function.
Switch, General-Use. A switch intended for use in general distribution and branch circuits. It is rated in amperes, and it is capable of interrupting its rated current at its rated voltage.
680.43 Indoor Installations. (C) Wall Switches. Switches shall be located at least 1.5 m (5 ft), measured horizontally, from the inside walls of the spa or hot tub.
680.22 Area Lighting, Receptacles, and Equipment. (D) Switching Devices. Switching devices shall be located at least 1.5 m (5 ft) horizontally from the inside walls of a pool unless separated from the pool by a solid fence, wall, or other permanent barrier. Alternatively, a switch that is listed as being acceptable for use within 1.5 m (5 ft) shall be permitted.
and it took 4 pages of discussion to get here ?????Let's assume for a minute that this Hot Tub is not even being fed from the panel in the picture.
I still say violation.
If a breaker in the panel pictured is the disconnect I still say violation.
If someone came out of this panel to a disconnect more than 5' away from the tub and then came back to feed the tub, I still say violation.
If the breaker in the panel is the disconnect for the tub and it was more than 5' away I say ok.
If the panel was out of sight and a disconnect was installed at least 5' away from the tub I say ok.
If there was a permanent barrier built between the tub and this panel or a disconnect that might happen to be closer than 5' where you couldn't reach the disconnect from the tub I'd say try to find a better place to put the tub, but, still seems it would be ok.