Usually there is a access area for the motor under the tub. We usually put the disconnects there.
680.12 Maintenance Disconnecting Means. One or more
means to simultaneously disconnect all ungrounded conductors
shall be provided for all utilization equipment other
than lighting. Each means shall be readily accessible and
within sight from its equipment and shall be located at least
1.5 m (5 ft) horizontally from the inside walls of a pool,
spa, fountain, or hot tub unless separated from the open
water by a permanently installed barrier that provides a
1.5 m (5 ft) reach path or greater. This horizontal distance is
to be measured from the water’s edge along the shortest
path required to reach the disconnect.
Those are items you are talking about are listed as disconnects, cabinet covers are not.
I am not arguing intent, just pointing out what the words they chose to use say.
Understand, and also realize some inspectors can be really strict in reading it.If it is behind the door is it in sight?
Again forget intent and what normally see and do, just read the words.
I don't expect anyone to change their SOP.
I don't think that qualifies as the codes states at least 5' away and no more than 50'.
Except for a few instances where the spa is custom built on site, isn't the entire packaged spa "the equipment"?The section requires in sight from the equipment not just the tub.
Except for a few instances where the spa is custom built on site, isn't the entire packaged spa "the equipment"?
I think you have to use a little common sense sometimes.
So for a typical packaged spa where do you put the disconnect so that you can see it at all times while you are working inside the primary service access that is also more then 5 feet away from the edge of the water?Too me commonsense says in sight from means in sight from.![]()
Though this thread is about hot tubs, a motor driven machine can still have motor driven components not in sight of the motor disconnect, this disconnecting means is about more then just the motor itself on such machines. Not all machines can have a disconnect within sight of all motor driven components.
As well as driven portions of the load not close or within sight of the motor? Disconnecting means is for the driven load as much as it is for the motor.I disagree, the motors that are out of sight would need their own disconnects.
As well as driven portions of the load not close or within sight of the motor? Disconnecting means is for the driven load as much as it is for the motor.
a majority of what is out there has just a disconnect near the motor. I can show you a lot of machines in just grain handling operations that have moving machinery far from the motor, I would love to be able to profit from putting several disconnects around said machines, but will be underbid by someone that only puts one near the motor - and he will still pass inspection.The NEC specifies a disconnect must be in sight from from the motor and the driven machinery. See 430.102(B).
In my opinion there is no limit to how many disconnects that might require.
a majority of what is out there has just a disconnect near the motor. I can show you a lot of machines in just grain handling operations that have moving machinery far from the motor, I would love to be able to profit from putting several disconnects around said machines, but will be underbid by someone that only puts one near the motor - and he will still pass inspection.
My mentioned references are at commercial grain elevators which are permitted and inspected - as well as at farms and more of those are being inspected then ever beforeI believe you 100%, that does not change my opinion of what the NEC requires.
Furthermore I am not sure I would use farms as example of wiring done well.![]()