I do not believe the perimeter surface which is the elevated deck is what is implied in 
(2)  Perimeter Surfaces.  The perimeter surface shall extend for 1 m (3 ft) horizontally beyond  the inside walls of the pool and shall include unpaved surfaces, as well  as poured concrete surfaces and other types of paving. Perimeter  surfaces less than 1 m (3 ft) separated by a permanent wall or building  1.5 m (5 ft) in height or more shall require equipotential bonding on  the pool side of the permanent wall or building. Bonding to perimeter  surfaces shall be provided as specified in 
680.26(B)(2)(a)  or (2)(b) and shall be attached to the pool reinforcing steel or copper  conductor grid at a minimum of four (4) points uniformly spaced around  the perimeter of the pool. For nonconductive pool shells, bonding at  four points shall not be required.  
If the hot tub was setting directly on the ground, asphalt or concrete then the 3 foot perimeter would come into play.