Hot tub

Status
Not open for further replies.
Right it’s the ground but there is no actual bond in the panel ! I didn’t install the panel it’s old but now it seems to be my issue
Sounds like you have some serious issues which could be dangerous for a hot tub. Can you provide some photo's of the panel, hot tub circuit, ETC.?
 
Also a low impedance meter, Solenoid tester is best for checking for “real” voltage in these scenarios.
Are you referring to a "Wiggy" as they were called way back when? I have seen electric utility linemen use two 60 watt incandescent bulbs in rubber sockets and test leads.
 
I don't understand this:
"i Installed 240v to a hot tub yesterday, with a disconnect using a single pole switch using the ground and the neutral to the switch"


Why have a sp switch on a 240 volt hot tub?
 
I don't understand this:
"i Installed 240v to a hot tub yesterday, with a disconnect using a single pole switch using the ground and the neutral to the switch"


Why have a sp switch on a 240 volt hot tub?
He is deliberately attempting to force a neutral to EG fault. The GFCI should trip. It failed to do do.

Relying on that as a disconnecting means is beyond belief.
 
He is deliberately attempting to force a neutral to EG fault. The GFCI should trip. It failed to do do.

Relying on that as a disconnecting means is beyond belief.
Why is that beyond belief? We’ve done in hotels with a push button emergency stop switch, it trips the gfi and shuts the whole system down!
 
I don't understand this:
"i Installed 240v to a hot tub yesterday, with a disconnect using a single pole switch using the ground and the neutral to the switch"


Why have a sp switch on a 240 volt hot tub?
It looks better than a 50amp disconnect! But it seems to me I’m going to have to put one in anyway and fix the ground in their house
 
I don't understand this:
"i Installed 240v to a hot tub yesterday, with a disconnect using a single pole switch using the ground and the neutral to the switch"


Why have a sp switch on a 240 volt hot tub?

His is using the switch to create a neutral to ground short so that the gfci trips.🤞
 
His is using the switch to create a neutral to ground short so that the gfci trips.🤞
Doesn't seem like a switch is listed for that use. Perhaps a push button in the commercial world, but not in residential. What is the wiring like? A 50 amp circuit with something like #12 taps off it to a switch? How is that being done?
 
I found in the main panel there is a ground coming from the meter through a grounded bushing straight to the cold water ground, no bonding in main panel nor not good continuity between main and sub panel !
In the OP you gave the answer. There is no bonding in the main panel. I would love to see a one-line of what you have there. From the sounds of it, there's no permit either.
 
Doesn't seem like a switch is listed for that use. Perhaps a push button in the commercial world, but not in residential. What is the wiring like? A 50 amp circuit with something like #12 taps off it to a switch? How is that being done?
The whole hookup is bizzare IMO.
 
Doesn't seem like a switch is listed for that use. Perhaps a push button in the commercial world, but not in residential. What is the wiring like? A 50 amp circuit with something like #12 taps off it to a switch? How is that being done?
I can’t believe you never heard of this ? I’m asking about the ground I’m not giving a tutorial of how I did the job , I’m going back Monday to redo a few things! But the ground is in question here not the switch!
 
In the OP you gave the answer. There is no bonding in the main panel. I would love to see a one-line of what you have there. From the sounds of it, there's no permit either.
No he did not have a permit but I told him he should have one and it will be inspected I’m going to bond the main panel and put a disconnect in I guess
 
This setup cannot be used as the required means of disconnect. IMO
In what world is turning a switch to the “On” position to deenergize equipment OK?
And the problem the OP is trying to solve proves that it’s unreliable.
 
I can’t believe you never heard of this ? I’m asking about the ground I’m not giving a tutorial of how I did the job , I’m going back Monday to redo a few things! But the ground is in question here not the switch!

I understand you are asking about the ground but when we see violations we bring them out because there are many members who read this forum that can be misled by the install if we don't bring it out in the open.
 
Am I missing something? What exactly does the bond have to do with no ground at the tub? The equipment ground in the 50amp circuit should be connected to the neutral bar in the main panel. The panel bonding has nothing to do with the equipment ground at the tub. If you were to remove the green bonding screw on a working main panel, it would not change any of the grounds of the circuits leaving the panel. The metal box (panel) would not be bonded, and floating. The circuit's equipment grounds would still function.
 
I understand you are asking about the ground but when we see violations we bring them out because there are many members who read this forum that can be misled by the install if we don't bring it out in the open.
Understood and that’s why I’m on here looking for the best fix
 