I hope you are just asking the OP if that's what he has and not thinking that your descriptions are correct.View attachment 2558876
Murr72 does this depict what you have in the service disconnect?
Yes there must be a MBJ in the service disconnect.The whole concept of having the MBJ start in the meter then hit the bond bushing in the service can got me looking in the code for where the MBJ has to be 100% in the service disconnect. And its 250.24:
Also keep in mind this is Chicago and everything would be EMT so probably no wire type EGC's.
Yes I am trying to clarify the above OP statements from post #1:I hope you are just asking the OP if that's what he has
Better. Now if you could show that bar floating along with all the other terminations...
No, not that I'm aware of. The municipalities in Cook and surrounding counties have their own ammendments and selected version of the NEC. In the Chicago Electrical Code, 250.80 requiring metal enclosures for service conductors and equipment to be connected to the grounded system conductor was lifted verbatum from the NEC. (Chicago code is based on the 2017 NEC with ammendments)All meter sockets, I've worked with, have the neutral secured to the can. Are Cook County sockets different?
In Chicago it is limited to existing residential occupancies of at most 3 units:Is SE cable allowed there?
Out of curiosity, how many dwellings have busways, cablebus or MI cable installed?No, not that I'm aware of. The municipalities in Cook and surrounding counties have their own ammendments and selected version of the NEC. In the Chicago Electrical Code, 250.80 requiring metal enclosures for service conductors and equipment to be connected to the grounded system conductor was lifted verbatum from the NEC. (Chicago code is based on the 2017 NEC with ammendments)
In Chicago it is limited to existing residential occupancies of at most 3 units:
View attachment 2558882
View attachment 2558883