(422.16(B)(5))
_______________________________________________________________
Submitter: Doug Boggus, City of Grand Prairie
Recommendation: Revise text to read:
422.16(B) Specific Appliances
(5) Water Heaters. Water heaters shall be permitted to be cord-and-plug
connected with a flexible cord identified as suitable for use on water heaters in
the installation instructions of the appliance manufacturer, where all of the
following conditions are met:
(1) The flexible cord is terminated with a grounding-type attachment plug.
(2) The length of the cord is not less than 610 mm (2 ft) and not more than
1.8 m (6 ft).
(3) The receptacle is accessible.
(4) The flexible cord is not subject to physical damage.
(5) The flexible cord has a temperature rating not less than that marked on
the appliance nameplate or in the appliance?s connection wiring compartment.
(6) The water heater is identified for cord-and-plug connection.
Substantiation: Throughout the US, jurisdictions are constantly approached to
allow water heaters to be connected to 120-volt and 240-volt power supply
through plug-and-cord connection in violation of 422.16(A) as such appliances
are generally not identified for flexible cord connection. The most commonly
proposed type cord is ?dryer cords? rated at 30-amperes for connections to 30-
50 gallon storage type units. This is because of local demand for a quick and
safe way to facilitate removal and replacement of such appliances. The
proposed wording is intended to set necessary requirements for installations
where cord-and-plug connection of a water heater is chosen as the connection
wiring method. Such specific requirements will allow cord manufacturers to
address this issue with properly rated cord insulation and connections while
also allowing manufacturers of water heater appliances to be able to allow a
connection method that is favored by both electricians and plumbers making
new installations and by plumbers and homeowners replacing such appliances.
Panel Meeting Action: Reject
Panel Statement: The submitter has not substantiated a need for an exception
to 400.8(1): ??cords shall not be used?as a substitute for fixed wiring of a
structure.? The panel notes that water heaters are often installed near other
heating equipment or in areas used for storage of tools and other implements
that can damage cords. They are infrequently replaced, have no vibration
concerns, and can be serviced in place. Cellar installation of water heaters may
also necessitate that the cord be plugged into a ceiling receptacle, requiring a
cord longer than proposed and increasing the risk of cord damage.
Number Eligible to Vote: 14
Ballot Results: Affirmative: 14