Also they have a lower ampacity for 240V then the 208V. With resistance elements the higher the voltage the larger the draw so that chart is wacky wrong...
Good question, if you look at 4500 watt three phase right below the highlighted single phase, it still says 25 amp overcurrent and 10 AWG conductor - yet a 4500 watt 240 volt three phase unit should draw about 10.8 amps.Does that say max overcurrent protective device? I am not sure that would limit the device to 25 amps.
Also they have a lower ampacity for 240V then the 208V. With resistance elements the higher the voltage the larger the draw so that chart is wacky wrong...
Not that it says exactly which model...
Heaters furnished with standard 240 volt AC, single phase non-simultaneous wiring, and 4500 watt upper and lower heating elements.
View attachment 13916
There are NO Relays, the top element has a double throw thermal switch and the bottom is a single throw Thermal Switch (TS).
Top TS feeds the bottom TS after the top is satisfied.
That says which element is the hard worker. Bottom.
When a heater can not sustain in cold weather, the bottom is bad.
View attachment 13917
4500w heaters you use 10/2 and sleeve with metallic flex from the wall to flex 90 connector on the heater.
The most important connection is the grounding wire, especially where metallic plumbing pipe is use.
Although it is fairly impossible for both elements to turn on at the same time, most of the time one of the TS contacts cease/weld fail.
That's usually a good indication the element is bad.
Top of the tank has Pressure Relief Valve which should be tested / cleared regularly to ensure the tank doesn't blow up if something fails.
About 5% of the one's I've tested are frozen.