House wiring in emt?

Status
Not open for further replies.
G

Guest

Guest
Re: House wiring in emt?

Good catch Bob. Does Chicago adopt the NEC and then add-on their own state & local code, or do they just go by state and/or local codes?

If I haven't said it before, that pipe sure looks nice, and it would be cool for any tweaking down the road.

I would presume the Chicago code (or Illinois code) would preclude using "BX" (AC) on the high-hats.

EMT would be a hassle on certain retrofits. How does Chicago handle retrofits?
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: House wiring in emt?

Wayne I do not know how their code is produced.

I do remember someone from that area saying the use of AC was very limited, even on remodels.
 
Re: House wiring in emt?

As far as strapping the pipe, you may not see it in the pictures, however, it is there. Flightline is a stickler for this, and hammering in some nail straps is no big deal.
 

russ

Senior Member
Location
Burbank IL
Re: House wiring in emt?

Chicago does have it's own code for strapping.
Most inspectors will cut some slack on the rough strapping that's going under the drywall, as long as the conduit is not floppy or sloppy

18-27-348.13. Supports.
Electrical metallic tubing shall be installed as a complete system as provided in Article 300. Each tubing length shall be securely
fastened in place at least every 7 ft (2.13 m) In addition, each tube shall be securely fastened within 3 ft (914 mm) of each outlet box,
junction box, device box, cabinet, conduit body, or other tubing terminations.
Exception No. 1: Fastening of unbroken lengths shall be permitted to be increased to a distance of 5 ft (1.52 m) where structural
members do not readily permit fastening within 3 ft (914 mm).

On remodels, if the walls are opened it has to be conduit. If the dry wall stays on the walls AC is the norm, a few might use FMC.
 

ryan_618

Senior Member
Re: House wiring in emt?

Originally posted by russ:
Chicago does have it's own code for strapping.
This kind of thing really bothers me. Does gravity act upon an object at the rate of 9.8 meters per second squared in Chicago like it does in the rest of the world? Oh it does? Then why the amendment?

I am not an electrical engineer, but if I were I would be furious at all these ridiculous local amendments. How are you supposed to design a system from your office in NYC for a job in Boston when they have an amendment to table 310.16? :confused: OOPS! I forgot...electrons move slower in Boston, right?

I'm sorry about the rant, but this morning I read in my local chapter of ICC newsletter about a local amendment that was passed 6 months ago and has now been repealed 180 degrees.

We have enough to worry about without stupid amendments like these. I challenge anyone to tell me why you would have to support conduit more rigidly in Chicago than anywhere else on the face of the planet. Any takers?
 

russ

Senior Member
Location
Burbank IL
Re: House wiring in emt?

I really don't have any idea where Chicago got 7FT from. For that matter I have no idea how the 10FT came about in the national. There are a lot of differences in the two codes and a lot of similarities.

If you design a building in Chicago, you have to buy their building code book and their electrical code book. It's the only way.

[ November 04, 2003, 08:21 PM: Message edited by: russ ]
 

wolfman56

Senior Member
Re: House wiring in emt?

Ryan,
You must understand, Chicago has been known as "The City That Works" (like a well oiled machine). Emphasis on "oiled". Nothing gets done in Chicago without a little "grease". It doesn't have to make sense just money!! There many strong union interests there, and all those extra codes add up to more labor and materials used. In Chicago if it's wire it shall be in conduit, even phone line! Now think of how close in proximity Chicago is to where most of the steel is made.
Rick
 

ryan_618

Senior Member
Re: House wiring in emt?

Russ: Thanks, and again sorry for the rant.

I just find it to be a joke that localities think they have to make their own code. It sure seems like a waste of time to me. If there are geographic issues than by all means, amend the code. Otherwise...do what 250 million other Americans do and leave it alone!!! :D
 
G

Guest

Guest
Re: House wiring in emt?

I would be interested to know what the per capita adoption rate for the NEC is vs. the non-adopted per capita. What percentage of the US population has chosen not to adopt the NEC at all?
 
G

Guest

Guest
Re: House wiring in emt?

I'm sure I can find it somewhere on my own. I'm hoping that I can stay in my Barcalounger while somebody hands me the answer on a gold platter :)
 

flightline

Senior Member
Re: House wiring in emt?

Watching this thread play out has been a bit of an experience. It has taken some turns as threads sometimes can. But I feel that I must set some things straight.

First, Chicago has always had their own electrical code. It is not some sort of local amendment as some have suggested or believed. Prior to 1999, it was completely different than the NEC and most other codes. In 1999, Chicago re-wrote it?s now arcane code to and based a large part of it on the current NEC. The Chicago Electrical Commission was tasked with re-writing the code at that time. It consists of the Chief Electrical Inspector, a professional engineer in the electrical discipline, an electrical contractor, a journeyworker electrician, a representative from the local utility, [Exelon], and the director of Fire Prevention. There are sections that are strictly Chicago such as high rise codes, plenum codes, and hospital codes. The new code is so written for the most part, to only recognize the metallic wiring methods. That being said, Chicago code does address things like NM cable, and other non-metallic wiring methods, but in so doing severely limits the scope of their use.

Second, I would venture a guess that the photos that Scott Moran posted are those of a house under construction in the suburbs, not the city; it may even be one I inspected in our town, but no matter. Now to that; we adopted the 1999 NEC, but limited the accepted wiring methods to those metallic ones recognized by the Chicago code. Russ?s area, I believe has adopted the Chicago code. I would look to change to that as well, as it weeds out some of the confusion in working between suburbs. As Scott has accurately stated, as an inspector, I am a stickler for strapping. I don?t whip out a tape measure to see if I can conjure up a violation, but I do believe that pipes should not rattle in a wall; nail straps are inexpensive, quick and easy to install.

To respond to ryan comments as to our decorated history with a number of disasters. That may be true, but I don?t believe that any of these could be directly attributable to the use of EMT as it is today. Even the recent fire at the county building where people died, and it is being touted as being started by a fluorescent fixture, as tragic as that is, I believe, will not speak to the EMT as being an issue.

What makes our codes as stringent as they are could be that we are the birthplace of the high-rise. We have ?2- of the tallest building in the US here in Chicago. There are other projects that too have been called the ?worlds ----?. And while ryan may feel it?s a joke that a locality may make up it?s own code, we are far from a ?locality?; for a long time being one of the top 5 largest cities in this country. What took place here required codes that addressed things that were not happening everywhere else. That being said, residential does happen pretty much every place else, but we do it our way, and it seems to work fine.

Both brianjohn and wolfman tout that this is a big union town, [area]. We are. I have been told that we are one of the largest IBEW locals in the country with between 9000 and 10,000 members. There are even more in the ?2- collar counties that are strictly pipe and wire. I?m one of those union members. We have our way of life, and you have yours. If I were to say that it takes more skill and talent to install EMT over NM, I bet you would be offended. I would grant you that to do a job well using whatever means of wiring you use is up to the individual or the contractor.

Ryan, I don?t think we?re going to take your advice and do what everyone else does; we?re still going to have our code. It seems that the contractors here can deal with those municipalities that use Chicago, those that use the NEC, and all the local amendments; we?re kinda? dynamic that way.

I try to be introspective and respectful when I write my posts; not believing what we do is better than someone else. That?s what I tried to state in my last post. Everyone is entitled to his or her opinion. I have read this post from beginning to end, and I believe that some of the comments posted here do not share in that mutual respect and have at times been sarcastic; perhaps I can?t tell since we can only discern tone from the words we see. I respect most everyone here as professionals whether they are a one-man band type of operation or the most degreed engineer. I would ask that since differences exist between areas, that we just accept that we cannot change. In that I mean, unless you live or work in our area, don?t bash it.
 

sjaniga

Member
Re: House wiring in emt?

Flightline,

I have been told by some that Chicago, being a big union town, has its restrictions on NM to keep homeowners from doing a lot of their own work. Is there any truth to that?

If so I think it is great and would like to see this implemented in our area, all to often I see homeowners attempting to do electrical jobs but wont even touch the plumbing because it is pipe.

Scott
Across the lake in MI
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
Re: House wiring in emt?

I can tell you that Chicago is not unique in having their own code. Being close to New York City I can tell you that that is the way it is there also. Unfortunately (or fortunately) I don't do any work there and I'm not familiar with how it differs from the NEC. Anybody here know? I believe pipe is required but not in residential.
 

flightline

Senior Member
Re: House wiring in emt?

In reply to Scott, [sjaniga], Chicago code has and still does not allow anyone other than a registered electrical contractor from obtaining an electrical permit. In so doing, homeowners are not allowed, [unless, that is, if they happen to be a registered electrical contractor]. It is up to the individual suburb as to what they do. Although being an inspector, I have less concern about the jobs that I do get to see, as opposed to those that I don't get to inspect. At that point, I guess home inspectors would have the good stories about DIY horrors.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: House wiring in emt?

Originally posted by ryan_618:
How are you supposed to design a system from your office in NYC for a job in Boston when they have an amendment to table 310.16? :)

But your conductors may be bigger than required.

Call it a home field advantage. :D

Truthfully MA did not amend 310.16, MA amended Table 310.15(B)(2)(a).

Bob
 

russellroberts

Senior Member
Location
Georgia
Re: House wiring in emt?

As to Flightline's comments about doing a house in emt,I've piped a few wood framed buildings,and it's a different ballgame alright.

Being a romex puller mostly,I have nothing but the utmost respect for an electrician who can pipe a house quickly and effeciently and pass inspection.

Russell
 