elecguy21 said:Can I put the 3 bedrooms recepts on 1 circuit? lights will be seperate.
I'm still curious about the service, are the two service disconnects going to be installed next to each other?
elecguy21 said:Can I put the 3 bedrooms recepts on 1 circuit? lights will be seperate.
Didn't I say that? :wink:elecguy21 said:Can I put the 3 bedrooms recepts on 1 circuit? lights will be seperate.
Do the 2 meter can's have 100 amp disconects built with them such as meter disconect combo type?elecguy21 said:Yes the 2 meters out side with a nipple to the first floor panel and a nipple to the 100 cb for second floor panel.
elecguy21 said:Yes the 2 meters out side with a nipple to the first floor panel and a nipple to the 100 cb for second floor panel.
infinity said:Now you have a problem. The service disconnects need to be grouped together. You can't have the 1st floor disconnect in the panel on the inside of the building and the 2nd floor disconnect on the outside. Take a look at 230.72.
haskindm said:Careful there. We are allowed to run a set of service entrance conductors to each occupancy per 230.40 Exception 1. Then 230.71(A) says that the disconnects FOR EACH SET OF SERVICE ENTRANCE CONDUCTORS may consist of up "not more than six switches..."
infinity said:Now you have a problem. The service disconnects need to be grouped together. You can't have the 1st floor disconnect in the panel on the inside of the building and the 2nd floor disconnect on the outside. Take a look at 230.72.
rbwsparky said:I always use metal 4X4 boxes with mudrings for all my receptacles and swiches. They ensure your decices will stay put forever.
What? :-? 'Splain, please.rbwsparky said:I always use metal 4X4 boxes with mudrings for all my receptacles and swiches. They ensure your decices will stay put forever.
elecguy21 said:Stickboy the meters will be in a 2 gang meter pan out side, going out the back of pan from each meter to the inside right into a 100a panel for 1 and either a 100a panel or a 100a cb for #2. No2 has an ac unit ,a furnace and a garage door open on first floor. Both apartments have 2 baths each and Iplan on using 1 20a cb for 2 baths. any thoughts on both of these wiring ways?