Watched it ! very good information there. I am very familiar with most of the info with exception to that it takes 5 to 6 times the rating of the cb to open, and that I clearly forgot to check to see if the main service was indeed bonded !!!! I took that for granted :happyno: who installs a service without bonding !!! I noted the ground rod, and GEC, and connection to the plumbing, but I didn't check to see if someone ran the GEC to the service also, and bonded the GEC to the neutral bus !!!!!! This would explain a lot. The "Forensic Expert" missed it too. He told me to run a new ground back to the service from wherever that wire was connected, and bond the plumbing where it was cut out. Thanks guys !! Feel better about how to tackle this now.The Grounding Electrode System has little to do with clearing ground faults or short circuits. Please watch this link, slides 10 -68 are critical. http://www.tirebiter.net/downloads/ludecke.html