As I do not live in, do electrical work, or have any UK spec appliances, I cannot answer the question. Ask for the restaurant grill, okay you got me there.
What are you really asking here in this topic? As far as I know, all things are wired, and have ocpd based on nominal system voltages. The only exceptions I'm aware of are motors, which are rated/ labelled 230 / 460 volts, presumably to account for voltage drop on 240 and 480 volt systems.
Most manufacturers base their ratings from nominal system voltages. Some, who knows, like your average air compressor for home use listed at 5 horsepower, but only draws 10 amps on 120 volts. I believe those ratings may be based on Startup or locked rotor current.... or simply wishful thinking. Many portable home generators have similar peak power ratings that are advertised, however their continuous or steady-state wattages are much lower
Take this for example:
32 amps at 208 volts single phase. Is 32 amps the current draw at 208 volts or 229 volts I guess I am asking.
The way that I interpret that name plate is that it draws 28.0A on 3 phase and 32.0 amps on single phase 208. The lower kilowatt ratings for single phase are not on the nameplate. single phase is probably a few amps higher though due to a motor or something running in addition to the heating elements. My wag for the day.
Eta: 32.0 amps appears to be the maximum amperage draw per phase.
all of the numbers appear to be based on 208 volts